I will be installing an A3 consumer unit for a customer in a hallway, and they are thinking of relocating a radiator directly below it. Assuming the maximum temperature of the rad is never likely to exceed 30'c, an MK technical tell me the operating temperature of their mcb/rcd is -5 - 40'c, I can't see it being an issue. Wouldn't have considered it before with plastic CU's, but was wondering if metal CU's would make a difference, my physics is not good?
 
I would expect the radiator, if a standard gas / electric boiler, would exceed 30°C however the ambient temperature of a consumer unit above it should not exceed 40°C.
With a metal enclosure there would be better conductance of heat into the interior and the DIN rail and earth bar, but overall the system will reach thermal equilibrium at a very similar state to a plastic CU.
The installation of a diverter plate below the CU would go some way to preventing a build up of heat in the CU, if you feel it necessary.
 
it will be OK as it's metal, non-combustible, it can survive being in the exhaust of the starship enterprise for 30 minutes to comply with fire regs. however, it will be radioactive for 30 million years, so wear a dust mask when disposing of it in an eco-friendly way (i.e.chuck it in the nearest dustbin).
 
I would expect the radiator, if a standard gas / electric boiler, would exceed 30°C however the ambient temperature of a consumer unit above it should not exceed 40°C.

The installation of a diverter plate below the CU would go some way to preventing a build up of heat in the CU, if you feel it necessary.
Sorry meant ambient temperature above the rad unlikely to exceed 30'c. Thought about a shelf. But worrying needlessly I think, if we get a good summer this year, the ambient temperature could reach at least 30'. :grin:
 
metal CU.....what could possibly go wrong? (apart from a "live" casing due to some dipstick mis-wiring the earths. tails shorting out, rust, oops. forgot it's amd3 compliant, must be OK.)
 
I'd guess they rate the ambient temperature at 40C because you'd need to apply derating factors to the tripping curves of the circuit breakers if that's exceeded. The actual materials inside a CU should be able to withstand way over 40C without damage.
 
I'd guess they rate the ambient temperature at 40C because you'd need to apply derating factors to the tripping curves of the circuit breakers if that's exceeded. The actual materials inside a CU should be able to withstand way over 40C without damage.

of course they will. amd3 ensures that they'll withstand 600 deg.C.,,being steel or concrete. :45:
 
I will be installing an A3 consumer unit for a customer in a hallway, and they are thinking of relocating a radiator directly below it. Assuming the maximum temperature of the rad is never likely to exceed 30'c, an MK technical tell me the operating temperature of their mcb/rcd is -5 - 40'c, I can't see it being an issue. Wouldn't have considered it before with plastic CU's, but was wondering if metal CU's would make a difference, my physics is not good?

Whats sort of Rad would that be, a very large one:confused5:


Cheers
 
If it's in an OAPs house then the 'altisphere' above the door frames can easily reach in excess of 80°C! Or that's what it sometimes feels like when you are changing over a fiddly light fitting in the middle of winter, especially in old Victorian 10ft high ceiling houses. In those circumstances I always strip down to my string vest. So, yes Mid, a shelf may be needed! Seriously though I wouldn't worry mate. Cannot see it being an issue in any typical house and in a hallway.
 
but if the metal CU is below 70 deg. C., how the hell are the customers supposed to dry/warm their coats on it?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Midwest

Arms
-
Joined
Location
Oxfordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
ambient operating temperature of consumer unit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Midwest,
Last reply from
Geordie Spark,
Replies
15
Views
5,046

Advert

Back
Top