Ackbar states the important fact, thermal effects. Whats the design of the cable run like E54?

Each to there own but as i say i'd have done it differently.
 
It's amusing this thread appearing, as I've been toying with exactly the same question for a while.

Personally, I can't see any practical reason not to - I haven't got the book with me to look up the figures to do the maths (and I'm sure you've done that already anyway!) - but it stands to logic that if 1 x 2.5mm will sustain a 20A radial, and 1 x 4mm will sustain a 32A radial then thats a factor of 8 - therefore if a 2 x 2.5mm ring is good for 32A then a 4mm one is good for 50A (subject to method, of course).
 
We have wired 4mm t+e ring finals on many occasions in domestic situations, due to the de-rating of 2.5 t+e running through 100mm + of loft insulation (in bungalows roof voids) thus enabling us to install the ring final on a 32a mcb/rcbo. I would be a bit dubious installing 40a protection though but I suppose it would depend on the installation method employed and external influences.
 
well just think heating elements and rcd/rcbo can give problems one appliance trips and youve lost the lot ,should be on radials
 
I agree with safety first in that if there is a fault on the circuit it is shut up shop time but can not see any other reason why not to run 4mm ring on a 40a as long as thermal effects are covered
 
E54 you sure the CPC is 2.5mm? 4mm T&E here in the UK is 4/1.5, not that it affects the discussion.

A 32A ring in 2.5mm has to have 20A current capacity on all legs. Not sure where the 20A for 2.5 comes from, but in Table 4D5 20A on 2.5mm compares to 26A on 4mm (ref Method A)

Using the 20/32 ratio, if you've got a minimum 26A CCC on each leg the OPD could be up to 41.6A. Could be higher if you know the CCC of each leg is higher.
 
I've seen 4mm rings with 2.5mm cpcs before. Wired in singles a long time ago before copper was so expensive.

However in your situation I would have thought dedicated radials would be the more obvious choice.
 
i think i've read this a bit differently to you lot. i thought he was saying the circuit has one 4mm leg & one 2.5mm leg. if so, i'd be inclined to treat it as a standard 2.5 ring, and drop the 40amp to a 32amp.
 
my 2p
there is no problem in doing a 40a ring in 4mm , seen it and done it in warehouses with a large floor areas.
but its the connected loads that are of concern.
is it not still standard practice to put loads of 3kw and above that are on for lengthy periods on individual radials ?
 
i think i've read this a bit differently to you lot. i thought he was saying the circuit has one 4mm leg & one 2.5mm leg. if so, i'd be inclined to treat it as a standard 2.5 ring, and drop the 40amp to a 32amp.

I think the 2.5 is the cpc
 
I would drop the RCBO to a 32a, but otherwise i dont see any problems. I wouldn't do a ring in 4mm, it will be real donkey work terminating the ends into the sockets, especially if there are any single gang one's.

Cheers...............Howard
and if there was loads of insulation under the floor Howard?....as in many newbuilds...
 
I think the 2.5 is the cpc
looks like you're right. it just seemed a strange question, as i've done a fair few 4mm rings, so they're not that unusual. i thought e54 must be throwing us a googly and trying to make us think.
 