That's funny, ...every US GFI breaker or GFI receptacle i've come across, and that a considerable amount, have always been clearly marked for 6mA!!!
Haha... we have a range of RCD devices, some come in an S type version, (time delayed) 10mA, 30mA, 100mA, 300mA, 500mA
We in Europe tend to protect complete circuits with RCDs, whereas accross the pond there, you tend to protect a load/appliance via a RCD receptacle, or a GFI breaker circuit with a specific single load. Imagine the level of nuisance tripping on for argument's sake, a receptacle circuit with an RCD breaker trip level of just 6mA!! lol!!
Also we ensure that installations are limited to having a maximum touch voltage of 50 volts, so that they are not lethal. ...lol!!! The easiest way of explaining that to you, is maximum values of ground rod protected systems linked to RCD devices. (As the states use a hell of a lot of TT systems ''Ground rod grounding'') So U =RI, say R=50v/0.3A (300mA) =167 ohm Max, ....or R=50v/0.1A (100mA) =500 ohms Max. I'll let you do the calc for a 30mA RCD...lol!!
Hope that makes some sense to you, as i'm not concentrating to well, ... i'm doing other things at the same time here at the moment...lol!!!