Charles Lill

-
Trainee
Reaction score
2
could anyone take a look at these figures please and tell me if they are ok or not. thanks in advance
watts where stated60w x 360w x 3
Ib design current1.301.30
In device rating and typeB6 MCB
BS 60898
B6 MCB
BS 60898
Reference method

METHOD
B
METHOD
B
Ambient
temp in ◦c
40◦c40◦c
Cable type/
insulation
90◦c
Thermo
setting
Single core non sheathed cables
90◦c
Thermo setting
Single core non
Sheathed cables
Ca ambient factor0.910.91
Cg grouping factor0.800.80
Length in meters12.5 METERS10.5 METERS
Max volt drop6.96.9
mV/A/m max3131
Size selected mm21.5MM²1.5MM²
It6.826.82
Iz(must be larger than In)8.248.24
Actual voltage drop0.27V0.22V
Max disc time0.40.4
ACTUAL Zs1.58
Max Zs as bs76717.28
7.28
 
Fair enough. Maybe give advice on how to find them....but why give the answers on a plate.....correct or not?

I will help anyone if I can, I actually wrote a big post yesterday ready to send it through on his PM like I have been doing with another member but unfortuantly he's either turned off his private messages or is account dont allow them. Didnt want to keep a thread dragging like we've seen before.
 
I will help anyone if I can, I actually wrote a big post yesterday ready to send it through on his PM like I have been doing with another member but unfortuantly he's either turned off his private messages or is account dont allow them. Didnt want to keep a thread dragging like we've seen before.
. Hi my apologies for all the threads
 
No worries Charles, my knowledge certainly is not that of most of the forum yet will help anyone when I can.
No worries Charles, my knowledge certainly is not that of most of the forum yet will help anyone when I can.
if you could possibly walk me through the assignment it would be appreciated my email is [email protected]
 

Reply to are these figures right or am i way off in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock