Hi,

I work for a generator manufacturer. We manufacture Automatic Transfer Switch panels for use with our generators, configured in the following way:

Mains and Generator supply are fed into an ATS panel containing interlocked (mechanically and electrically) contactors. The load side of the contactors are looped and the cables are then connected to a circuit breaker which feeds the distribution board/consumer unit. Three phase or single phase the set up is the same.

Does anybody have an opinion as to whether this is unsafe? I recently read a question (pasted below in italics) raising the issue of prospective fault current on the mains supply and that the mains contactor should be replaced with a circuit breaker.


Contactors are purely designed to switch a load (turn it on or off). They generally have a low Fault Current tolerance. Circuit Breakers are also designed to switch loads but can withstand greater Fault Currents.

For an ATS, a contactor is acceptable "on the generator side" (very low prospective fault current). The only way a contactor can be SAFELY used on the SUPPLY side is if the supply contactor is adequately protected by HRC fuses (minimum BS88), which can make this scenario prone to "nuisance trips". Therefore, the only solution is to use a circuit breaker for the supply protection (cheaper than a contactor) & to also make sure that adequate seperation between the generator supply & the incoming supply, is adequate. This is done to prevent magnetic affects from affecting the contactor under "fault" conditions.



I would appreciate your opinion on this question.

Regards,

Genset
 

Reply to Automatic Transfer Switch in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm an electrical engineer in training so please bear with me. Basically, a bank has ordered a second 500kw diesel generator and my job is to...
Replies
3
Views
865
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
837
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
504
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
Just joined as DIY homeowner. I plan on buying a 10KW backup portable generator and using a transfer switch on the house in Riverside County. As...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock