Tell the Plumber he is a ****.. Change the light.. Dont install RCD (Unless they are happy to pay) get paid go home.. Job done

As above like for like is a replacement and not addition therefore providing Ze and Zs are there then id be happy to crack on..
 
You will also need to ensure all other requirements are met to allow the RCD install.

Sorry just read that and I'm not a 'domestic' spark...........still learning everyday though lol.

I have to ask tho Hants............why would "all other requirements" need to be met to (allow) an RCD install ?
New one on me that to be honest ?
 
Change light

Take money

Inform them of the situation

If your loosing sleep issue a MWC and note the missing bonding/rcd situation
 
Sorry just read that and I'm not a 'domestic' spark...........still learning everyday though lol.

I have to ask tho Hants............why would "all other requirements" need to be met to (allow) an RCD install ?
New one on me that to be honest ?

I was reading the OP's comment as a light in a special location with no supp bonding or RCD, therefore just ensuring main bond is suitable, no more :)
 
I was reading the OP's comment as a light in a special location with no supp bonding or RCD, therefore just ensuring main bond is suitable, no more :)

Why would "all other requirements" need to be met to (allow)/install an RCD tho?
What requirements?
I'm curious:)
 
In that situation I would just advise on the benefits of RCD protection.....but I wouldn't let the decision stop me from changing a chuffing light fitting! Mind you.....how far do you go, I'd assume none of the other circuits supplying the bathroom are RCD'd either. I know........just recommend a CU change and full rewire. ;)
 
Why would "all other requirements" need to be met to (allow)/install an RCD tho?
What requirements?
I'm curious:)
As I reading the situation here, we have a job being carried out in a special location (albeit a light change) the plumber has removed the supp bonding and the circuit in question has no RCD protection. The requirements to allow the removal of supp bonding are to ensure the main water is bonded, the circuits are RCD protected and disconnections time met. I would of replied earlier but turning into a bit of a light weight and went to bed :)
 
As I reading the situation here, we have a job being carried out in a special location (albeit a light change) the plumber has removed the supp bonding and the circuit in question has no RCD protection. The requirements to allow the removal of supp bonding are to ensure the main water is bonded, the circuits are RCD protected and disconnections time met. I would of replied earlier but turning into a bit of a light weight and went to bed :)

Ahh I understand what you mean now mate your original post had me confused what you meant.

(You will also need to ensure all other requirements are met to allow the RCD install.)
 
How? Surface cabling from the light to the radiator. I think not.

Its a simple change of accessory.

Sorry mate that wasn't directed at you...............it's what someone did on another thread where there was no main bonding I just don't agree with it that's all lol
 
I believe only work carried out in zones within a bathroom is classed as special location
That is correct.
since part P changes earlier this year.
It was the same before.


In this thread, surely the plumber is irrelevant.
If you change a light for a customer and notice there is no supplementary bonding or RCD all you can do is advise the customer of the situation.
 