Having looked at previous posts just after some clarification.
If i am replacing a bathroom light like for like i don't need to put on an RCD?
If i am replacing one bathroom light with 2 or 3 IP rated spotlights i have to put on RCD as i have altered the circuit?
Cheers
 
If i am replacing a bathroom light like for like i don't need to put on an RCD? agreed
If i am replacing one bathroom light with 2 or 3 IP rated spotlights i have to put on RCD as i have altered the circuit? i would as i'd be supplying a MWC with my signature on it. CYA


 
No not correct IMO, RCD protection for all new bathroom equipment installed.

are you sure? "additional protection shall be provided for all low voltage circuits". So not ELV then ;)

If the lights in the bathroom are now SELV I can't see any practical reason to demand the LV circuit is RCD protected.
 
are you sure? "additional protection shall be provided for all low voltage circuits". So not ELV then ;)

If the lights in the bathroom are now SELV I can't see any practical reason to demand the LV circuit is RCD protected.

A grey area IMO regarding Selv
 
A grey area IMO regarding Selv

I agree. I guess my approach is that, if I am installing a new bathroom light circuit then I would RCD protect it, SELV lights or not. However if I was adding SELV lights to an existing circuit I would not insist on adding an RCD.
 
Surly it depends on if the bathroom has adequate supplementary bonding. If so then no you don't need to RCD protect but if not then the regs require all circuits in a bathroom to be protected by a 30mA RCD. As you are making an alliteration to an existing circuit that circuit must be left by you up to the current regulations as you take responsibility for that circuit.
 
Surly it depends on if the bathroom has adequate supplementary bonding. If so then no you don't need to RCD protect but if not then the regs require all circuits in a bathroom to be protected by a 30mA RCD. As you are making an alliteration to an existing circuit that circuit must be left by you up to the current regulations as you take responsibility for that circuit.

I think you might have that the wrong way round.......
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Bathroom Lights on RCD
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
wolfboy,
Last reply from
haj,
Replies
12
Views
6,125

Advert

Back
Top