Looking at instructions for installation for Baumatic BHI300 it requires a 20A Double pole (3mm separation) switched fused spur, I quote pretty well verbatim from the pdf manual! I have never heard of such an accessory, but I have lived a sheltered life and willing to be surprised. Anyone heard of this? Didn't think so.
 
  • Funny
Reactions: nicebutdim and DPG
I’m sure it’s not possible the fuses only go up to 13 amp , you can get double pole 20 amp isolators
 
  • Like
Reactions: Vortigern
Yeh I was wondering if that is what they meant, just a 20A (at least) isolator with a 20A MCB just badly written. I intend to ask the obvious question today of Baumatic customer support, should be amusing/educational.
 
Good luck with "Customer Support"! In my experience they will know nothing...and will say that if you don't follow the instructions the warranty will be void...
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Vortigern

Arms
~
Joined
Location
South West
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
F. H. Electrical

Thread Information

Title
Baumatic two zone induction hob - Needs a 20A double pole switched fused spur...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Vortigern,
Last reply from
pirate,
Replies
3
Views
1,127

Advert