I would suggest neutral on the faulty leg is interconnected with a neutral of another circuit (likely to be cooker). I am assuming you only removed the circuit in question to carryout the testing. Therefore leakage back through other neutral to earth at transformer. I would suggest removing faulty neutral and carrying out test between that and the neutrals of the other circuits on that RCD.