Discuss Bizarre dead short between Neutral and Earth in the UK Electrical Forum area at ElectriciansForums.net
I would suggest neutral on the faulty leg is interconnected with a neutral of another circuit (likely to be cooker). I am assuming you only removed the circuit in question to carryout the testing. Therefore leakage back through other neutral to earth at transformer. I would suggest removing faulty neutral and carrying out test between that and the neutrals of the other circuits on that RCD.
I've tested for borrowed Neutrals between other circuits as this is what I first suspected. Also, whilst the circuit was removed I tested for continuity of both Neutral legs to the main earth bar of consumer unit and nothing :thumbsup
Does it the circuit trip under load?
Nope, not a single trip and circuit has been under normal daily usage
Thanks for all your help everyone, much appreciated as always.
Erm, quite possibly?
So whilst the IR reading was low enough to require further investigation and rectification there may have been enough resistance between Neutral and Earth to not trip the RCD.
The thread title is "bizarre dead short"we will have to call you 2shortcircuit from now on :smile:
Your reading has only confirmed that you dont have a million ohms,add a bit of resistance of the cpc back to the met and its not that bizarre I would say for the rcd to hang on in there
That will be fine just write down for 'Design ' Electrical Trainee and Signed of by NICEIC supervisor ..Of course I am being flippant..? ' Tony Cable'..my autobiography I woke after 5 weeks from a coma...To find myself as an Electrician lol
It would seem you have hit the nail on the head.
The earth leakage is obviously working within the tolerance of the 30mA RCD therefore not tripping it however at a later date this could become worse and lead to nuisance tripping or the amount of leakage combined with that of other circuits could eventually step out of the tolerance level again causing nuisance tripping.
At least my actions of finding and rectifying the fault were correct and should eliminate any tripping of the device.
**** note to myself, Learn more, test more and understand more ****
Thanks again to everyone that has added their input, great forum.... I continue to learn more everytime I log on:thumbsup
Reply to Bizarre dead short between Neutral and Earth in the UK Electrical Forum area at ElectriciansForums.net
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...