Hi Guys, between N+E the max voltage should be at max 2V, so this sounds very much like a broken neutral somewhere or a badly connected neutral at the CU. my first test would be to check this out. I have this as a common problem here in Africa, especially when we have to use auto transfer switches between the mains incomer and the standby generator and the contacts become pitted and carbonized. So turn off each circuit at the CU, then test for a V between N+E, if it has stabilized and you are getting the correct readings turn on each circuit one by one until you identify the circuit that is giving you the problem.
Hope this helps.
 