Not sure what to do here. I am wiring detectors for someone, boiler is in a small cupboard in the bathroom. Too small to fit the detector as it won’t be 1-3m away & I can’t fit it in the bathroom. What’s best, to fit it outside the bathroom? Stupid place to have a bloody boiler!
 
Carbon monoxide detector doesn’t have to be mains powered or interconnected with smokes afaik.

Use a battery one and put it in bathroom.


How well ventilated is bathroom regarding windows and forced ventilation?
 
Does it say that in the MI?

Not debating, it’s very likely… but the MI will tell you for sure.
I'm now wondering how many CO alarms you have incorrectly installed

BS EN 50292:2023 would be my source of information and not the MI although all the MI's I have seen exclude bathrooms or areas with a high humidity level.
Given that the CO detector contains an electrochemical sensor it is understandable why they are not suitable for bathrooms and are more likely to give false alarms if installed in such rooms
 
Like I say, I wasn’t arguing the point… you’re probably right…. But I wondered what MI would say.

I have never fitted a co detector in a bathroom, as I’ve never come across a boiler in a bathroom…

I tell a lie. We used to get static caravans with boiler in a cupboard in the bathroom…. But I can’t remember now where the detector was located.
 
Unfortunately my boiler is in the bathroom. Whoever had the house before me did some DIY frame and doors. Fortunately it meant I could fit a battery powered detector at the very top opposite the boiler wall.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Boiler in bathroom/Carbon Monoxide detector
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
SSE,
Last reply from
KungFuTurkeyLeg,
Replies
6
Views
966

Advert

Back
Top