Hi

We are having a new kitchen installed and have changed ll the sockets / switches to a stainless steel (Like below)


There is a boiler switch below the boiler which i cant seem to find a switch for. Can i just use a fused spur? any advise would be great. I have found 3 pole switches but they all say "fan isolation" on them

20210422_075142_resized.jpg
20210422_075150_resized.jpg
20210422_075157_resized.jpg
 
You might need to get an electrician to trace what all the cores are doing.
Normally there is just a switch fuse that isolated the entire heating system.

I don’t think I’ve ever seen a 3 pole isolator on boiler circuits??
 
I suspect the 3 pole switch has been used to replace a programmer that would have originally been there.
The simplest fix is to fit another 3 pole fan isolator.

If the adjacent spur is the sole supply to the heating system (can't see any sideways interconnection) or if there is a single spur supplying the heating elsewhere, then the 3 pole could probably be eliminated by using connectors then just have a blank fitted over, checking would be required.
 
Last edited:
T
I suspect the 3 pole switch has been used to replace a programmer that would have originally been there.
The simplest fix is to fit another 3 pole fan isolator.

If the adjacent spur is the sole supply to the heating system then the 3 pole could probably be eliminated by using connectors then just have a blank fitted over, checking would be required.
Hi

So that is a 3 pole switch? ill just buy one that says Fan its thats the case
 
T

Hi

So that is a 3 pole switch? ill just buy one that says Fan its thats the case
You might be able to find one that has no writing on it.

As suggested above though... if the 3 pole isolator isnt actually doing anything... (do you turn it on and off frequently? is the whole heating system also isolated elsewhere?) then you could joint through each switch and cover with a blank plate in the decoration you need...

Advise: If your changing these to metal, then you might need to earth the plate
 
You might be able to find one that has no writing on it.

As suggested above though... if the 3 pole isolator isnt actually doing anything... (do you turn it on and off frequently? is the whole heating system also isolated elsewhere?) then you could joint through each switch and cover with a blank plate in the decoration you need...

Advise: If your changing these to metal, then you might need to earth the plate
I've purchased the below. Will this be ok do you think ?

 
I've purchased the below. Will this be ok do you think ?

need a perfect skim on the wall.perfectly flat or your switch will keep falling off. flatplate.... spawn of the devil.
 
Provided it's wired to simply call for heat/water or not, which is most likely, then that 10A switch is fine - most heating programmers only have contacts rated at 3amps anyway.

It would be interested to know if there's a fused spur elsewhere for the boiler, and whether it has a wireless programmer/time clock as many do these days. Do you ever use that switch?
 
It will be to isolate the boiler locally, assume the heating controls and wiring Centre are elsewhere with their own isolator. So there will be a permanent live, neutral and a switched live for the boiler. That 3 pole isolator most likely is to disconect those 3.

EDIT although looking at the photo again, I'm not so sure.....
 
Last edited:
I'm not 100% sure either. I'm not sure any of us can be without a closer look at what's going on there.
But In a sense it only matters either way if the switch rating matters.

Permit me to ask a silly question which I accept I should know the answer to:
Are you allowed to stick a 10amp rated switch on a (probably) 13A fused spur with a known load on the basis that it will never draw anything approaching 10amps most of the time (fan and pump really) and the switch would only have to survive long enough in fault conditions to blow the upstream fuse. A similar principle to 433.1.1. But I can't recall ever noting this being allowed. I also don't have BBB here to consult and my default position would be "no".
Anyone?!

(I also note that triple pole 20 amp switches marked boiler are practically non existent, though there are double pole 20 amp ones out there. )
 
I'm not 100% sure either. I'm not sure any of us can be without a closer look at what's going on there.
But In a sense it only matters either way if the switch rating matters.

Permit me to ask a silly question which I accept I should know the answer to:
Are you allowed to stick a 10amp rated switch on a (probably) 13A fused spur with a known load on the basis that it will never draw anything approaching 10amps most of the time (fan and pump really) and the switch would only have to survive long enough in fault conditions to blow the upstream fuse. A similar principle to 433.1.1. But I can't recall ever noting this being allowed. I also don't have BBB here to consult and my default position would be "no".
Anyone?!

(I also note that triple pole 20 amp switches marked boiler are practically non existent, though there are double pole 20 amp ones out there. )

Don't forget you use 20 Amp switches in kitchens for example. What's the OCPD rating in that case?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Boiler Switch
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
Jamesa2487,
Last reply from
timhoward,
Replies
25
Views
6,140

Advert

Back
Top