Okay fair enough, I think we are singing from the same hymn sheet here, when designing a sub-main we go through the assessing compliance bit when we are selecting our cables, and no I wouldn't try to make up the csa as a mix.

I was taught that where PME conditions apply that we allow for the worst case, and the CPC should be calculated separate from the MPB, so if the armourings would have been marginal for the MPB (just complying), then either use an extra core for the CPC or if large enough csa the core as the MPB, and use the armourings for the CPC.

I will have to look in the 16th ed and see if there was an actual reg for this, or if my then old boss was just belts and braces. :)
 
Arghh! we don't, either the core complies, OR the armourings comply for a "straight" CPC, that is what we have been saying, the armourings are earthed for protective reasons where a core is used as the CPC, NOT to make up the csa.

Sometimes we use a core for a bonding conductor, and the armourings as the CPC, so long as both comply csa wise for their respective functions, ie. as two separate protective conductors, both (in their own right) fulfilling two different roles.

What's the problem with using the core for both?
 
What's the problem with using the core for both?

Of course you use a core for both if a core is available, if no core is available then you use the armour for both.

I really don't understand how so many people manage to complicate such a simple issue.

If a submain is required to include a main bond you size the cpc accordingly. You cannot install a seperate conductor and then make one conductor operate as a bond and the other as a cpc, they're joined together at both ends!
 
Of course you use a core for both if a core is available, if no core is available then you use the armour for both.

I really don't understand how so many people manage to complicate such a simple issue.

If a submain is required to include a main bond you size the cpc accordingly. You cannot install a separate conductor and then make one conductor operate as a bond and the other as a cpc, they're joined together at both ends!

Just one rather big problem with that, you'd need a 2 core 70mm SWA to provide a near suitable CSA of steel wire to give you the minimum 10mm equivalence of a copper main bonding conductor!!
 
I'm just bumping some threads in the Electrical Forum, don't mind me while I do this, you don't have to respond to them. Although if they are still current topics, and you do wish to reply, you're welcome to. Keep the thread on-topic and make sure you stick to the forum rules though.
 

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
925
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock