Trouble is Tel when I do that I tend to get my self into all sorts of trouble, but that's the way to do itscousers never were ones to use euphemisms. tell it how it is . straight and to the point.
in actuality, we don't have an indoor shower. ours is a hosepipe and a colander in the back yard.
shoebox??? bloody luxury. last week's liverpool echo as a roof. kept the rain of as it was soaked in chippy grease from having wrapped last night's chips.We were lucky.
BOLLOX 2 U... 9.5kW/230V=41.3ABOLLOX. 9.5kW = 39.6A . 6mm clipped direct on a 40A or 45A MCB.
BOLLOX 2 U... 9.5kW/230V=41.3A
if you read Linksy5 comment Cables buried in wall not clipped direct
Surely you know about voltage drop