• Electrician Forum
    Welcome to Electrician Forum. We started out on April 22nd 2006 and used Electricians Forums as our brand name which is an unregistered trademark.
N
nickblake
My brains switched off chaps and i can remember how to calculate 3 phase kva
i know its V x I x 1.73 / 1000
so is it 230 or 400 x I x 1.73 / 1000
fee a right numpty cant belive ive forgotten it not done 3 phase calcs for a while please enlighten me to the correct figures then ill give my self a good slapping:D
Example 1
A 415 volt, three phase generator provides 200 Amp. Calculate the kW and kVA of this generator.
kW = V x I P.F. x ÷ 1000 = 415 x 200 x 0.8 x 1.732 ÷ 1000 = 115 kW
kVA = kW ÷ P.F. = 115 ÷ 0.8 = 143 kVA
Example 2
To calculate the current (Amps) available from a 150 kVA generator at 415 Volts
kW = V x I x √3 ÷ 1000 Therefore I = kVA x 1000 ÷ V x √3 = 208 Amps
Example 3
To calculate the size of a generator required to provide 150 Amps @ 440 Volt
kW = V x I x  ÷ 1000 = 440 x 150 x 1.732 ÷ 1000 = 114 kW
VA = √3 x Vl xIl
since VA = watts/PF
edit and it will be 400V
Thanks guys the pennys dropped im in the process of giving myself a slap ,im a right bleary eyed parrot faced wassok duuuuuu
Calculating 3 phase kva
Electrician Forum
nickblake,
nickblake,