When there is a lightning strike there can be a huge voltage difference between the local rod earth and the voltage at the earth of the local transformer. Also the overhead cable is a huge aerial with the N earthed at the local transformer, these effects combine to make for a huge N to E spike that could jump a small gap...
 
Are you planning on removing standalone 100ma when doing board upgrade.? Was it type s.?

It is a 100ma DP type S, so it will stay and a couple of 30ma RCD's on the new board or maybe even RCBO's. I haven't really thought too much about the board change at the moment as I am snowed under.
 
When there is a lightning strike there can be a huge voltage difference between the local rod earth and the voltage at the earth of the local transformer. Also the overhead cable is a huge aerial with the N earthed at the local transformer, these effects combine to make for a huge N to E spike that could jump a small gap...

Thanks I figured that it was something like this I was just looking for clarification that I was thinking along the right lines. There was obvious signs on heat on the insulation of the neutral. I took a picture which I will try to post, so that people can see how small the hole in the insulation is.

image.jpg
 
Problem fixed.
Got a CU change out of it as well, as I explained to the home owner that the current situation with the standalone RCD protecting all circuits is not the best solution plus the current CU is a mess and really cramped and some other bits and bobs, so turned out to be a nice little earner for a Sunday callout.

I will take a look at the surge protection as suggested. So thanks for all your helpful suggestions and a satisfactory conclusion.
Handy stuff that lightning. If you'd go round there to quote for some minor work, bet they would never of gone for a new CU etc. Its opened their eyes.
 
Handy stuff that lightning. If you'd go round there to quote for some minor work, bet they would never of gone for a new CU etc. Its opened their eyes.

Yeah it's turned into a nice little earner and it's nice to get good feedback. They made a comment about me being really thorough compared to other electricians they have had in the past.
 
Last edited by a moderator:
Yeah it's turned into a nice little earner and it's nice to get good feedback. They made a comment about me being really thorough compared to other electricians they have had in the past.

Hi Vitesse - I cropped your last post due to the fact you gave a little to much info' out regarding your customer, a quick search, plus your general location could easily have identified your customer, this info could have been used malicously. Lets just say he's in the force and leave it at that.
 
Hi Vitesse - I cropped your last post due to the fact you gave a little to much info' out regarding your customer, a quick search, plus your general location could easily have identified your customer, this info could have been used malicously. Lets just say he's in the force and leave it at that.

Ok no problem. My mistake, should have thought about that. Thanks.
 