My boiler is currently plugged into a double 13A socket in my utility room. I want to move this connection to an FCU and add an extra double socket. As a general rule, I try to incorporate additional sockets and FCUs into the ring rather than via spurs, but the cabling that feeds the existing double socket is not long enough and replacing this cabling would require major disruption to the room above.
If I replace the existing socket back box with a deeper version, is there any issue with extending one of the ring cables via a 3-conductor terminal strip in the rear of the box?
Alternatively, is it OK to run a spur cable to the new FCU and then run a spur cable from the FCU to the new double socket?
My boiler is currently plugged into a double 13A socket in my utility room. I want to move this connection to an FCU and add an extra double socket. As a general rule, I try to incorporate additional sockets and FCUs into the ring rather than via spurs, but the cabling that feeds the existing double socket is not long enough and replacing this cabling would require major disruption to the room above. If I understand your proposal correctly.
Providing the double socket you intend spurring from is part of the RFC and not a spur, of course the new 13Amp twin socket will be limited by the fact that the FCU will have a maximum 13 Amp cartridge fuse.
What I meant was adding a spur to the new socket from the input side of the FCU. The fuse in the FCU would thus only protect the feed to the boiler.
I know you can't daisy chain multiple sockets via a spur, but I wasn't sure if you could do this with an FCU and a socket.
Then No that would not be compliant
That looks like quite a neat solution. I note that you have linked to a crimp that only takes 1.5mm2 wire and has a 19A rating (voltage rating is not quoted), but I guess that more suitable crimps are readily available.
Yes there are various types and sizes suggest you Google "electrical crimps " to view the range, please do not do as you suggested with the FSU and the twin socket outlet, which I described as non compliant.
My preference was always to incorporate the FCU and new socket into the ring, so I'm pleased that no one has an issue with extending the cable. The spur idea is now dead.
use push-in wagos or ideal butt connectors for your connection.
wago...
ideal butt connector.....
shopping
Southampton