Good morning boys, its a good subject this one,:6: having read all the posts here s one( if i can load it on the screen) is a picture from a site I tested the last electrician decided to cut off all the bajos that had been joined together thus removing the earth path of the ring yes PME site with plenty of earth rods iphone 074.jpgiphone 076.jpg so he got confused about earthing leaving swa cables unprotected (204 was replaced )
 
Monkey - can you clarify. Do you mean that the SWA supply is on the PME and each hook-up box is TT'd (that's what I think you are saying)?
 
Hi wirepuller I have introduced back and stopped it at the point were the caravans join the supply!

Yep, ....All your doing there is, maintaining the continuity of the PME's SWA earthing system, your not incorporating any fly leads from those banjo link connections...
 
Last edited by a moderator:
Thanks for clarifying Monkey. Sounds good to me.

I label my Hook-up boxes with a warning about the earthing type, just in case some muppet 'looks at it' sometime in the future - can't say they weren't warned about what has happened!
 
New posts

Reply to caravan park tt system and earth rods in the Australia area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
918
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock