Bad as they are, the cables are not supported or correctly fixed therefore I would say it merits a C3. The block connector though would be a C2 which also includes basic insulation external to a suitable enclosure. How high is the distribution board fixed? Are these connections live and are they accessible?
The ESC guide below should provide some guidance.
View attachment 14051