Or spur programmer from a separate source,using outputs to switch relays, live and 2 switch lines. That should be possible. Never interconnect 2 circuits.
 
Or spur programmer from a separate source,using outputs to switch relays, live and 2 switch lines. That should be possible. Never interconnect 2 circuits.
 
Presumably 3c and e was used as pl n ch hw. So he’s lost a sw line due to cpc being reinstated
 
The nub of this is doing away with the N in the 3c+E that is difficult to replace.

If the programmer has fully isolated volt-free contacts, you can power it from one circuit while controlling another. The programmer L & N would be sourced locally, while the 3C+E brings a PL from the boiler circuit to the contact common and returns the CH and HW outputs. Two circuits would be present in the programmer and there is a risk of later alterations accidentally linking the circuits together. Not sure how you would address those risks in a domestic install.

Or, if the programmer doesn't provide isolation between the contacts and supply L, or to avoid two circuits in the programmer, you would need to add relays as per above. Power the programmer locally, use the 3C+E to send CH, HW & N to near the wiring centre, where two relays control the boiler circuit. Now the two circuits are present in the relay box instead, which can have suitable prominent labelling, and the separation is less likely to be breached.
 
can I had, if another gas engineer turns up ,boy he would not like that having two sauces of power ,either rip out and start again and sod the tiles or work under Neath the flooring .e.g. plaster board if possible .
 
Just to add something else [And haven't wired a Y plan for ages so could be wrong], but don't you also need a switched 'HW off' core from the programmer on a Y plan too ? If so that would be six cores in total.:rolleyes:
 
Just to add something else [And haven't wired a Y plan for ages so could be wrong], but don't you also need a switched 'HW off' core from the programmer on a Y plan too ? If so that would be six cores in total.:rolleyes:
I read it as the OP needed 5 cores to the boiler not the programmer. If it is the case that you describe then he could install a relay. Use HW on to energise the coil and wire the grey of the mid position valve and normally open of the cylinder thermostat to normally closed of the relay.
 
I read it as the OP needed 5 cores to the boiler not the programmer. If it is the case that you describe then he could install a relay. Use HW on to energise the coil and wire the grey of the mid position valve and normally open of the cylinder thermostat to normally closed of the relay.

I probably misunderstood Lee, it's that time of day when my old brain has had enough. :D
 