The nub of this is doing away with the N in the 3c+E that is difficult to replace.
If the programmer has fully isolated volt-free contacts, you can power it from one circuit while controlling another. The programmer L & N would be sourced locally, while the 3C+E brings a PL from the boiler circuit to the contact common and returns the CH and HW outputs. Two circuits would be present in the programmer and there is a risk of later alterations accidentally linking the circuits together. Not sure how you would address those risks in a domestic install.
Or, if the programmer doesn't provide isolation between the contacts and supply L, or to avoid two circuits in the programmer, you would need to add relays as per above. Power the programmer locally, use the 3C+E to send CH, HW & N to near the wiring centre, where two relays control the boiler circuit. Now the two circuits are present in the relay box instead, which can have suitable prominent labelling, and the separation is less likely to be breached.