G GLENNSPARK Jan 29, 2012 #16 find out what the ratings of these loads are and assess if the existing cable is up to it as well..using the diversity calcs in the OSG
find out what the ratings of these loads are and assess if the existing cable is up to it as well..using the diversity calcs in the OSG
A a1guvner Jan 30, 2012 #18 GLENNSPARK said: should be RCD`d really....special locations... Click to expand... Kitchen? you sure
E ezzzekiel Jan 30, 2012 #20 kitchens are not recognised by bs as special locations but are by building regs, rcd required but there is allready one fitted going by picture
kitchens are not recognised by bs as special locations but are by building regs, rcd required but there is allready one fitted going by picture