Hi guys,

I have heard on the grapevine that the regs have changed regarding main protective bonding conductor to gas and water supplies.

I understand the regs are that the clamp should be within 600mm of the stopcock or shut off valve or at point of entry.

Somebody has told me that you can now put the clamp at any point on the pipe as long as it is visible. is this true?? can someone shed some light on this??
 
Hi guys,

I have heard on the grapevine that the regs have changed regarding main protective bonding conductor to gas and water supplies.

I understand the regs are that the clamp should be within 600mm of the stopcock or shut off valve or at point of entry.

Somebody has told me that you can now put the clamp at any point on the pipe as long as it is visible. is this true?? can someone shed some light on this??

From memory i think it states "preferably within 60mm of the point of entry on the consumer side". Remember, the regs are a GUIDANCE document, not the law. It is more important that the bonding is installed and effective, than where it is connected. You will not get lynched if the bonding is not within 600mm, but you might if it isnt there at all.

Cheers............Howard
 
Paddy,

Regs 17th Ed 544.1.2 states:

'The main equipotential bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises. Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer's hard metal piework and before any branch pipework. Where practicable the connection shall be made within 600 mm of the meter outlet union or at the point of entry to the building if the meter is external.'

Memories can be fallible things and suppositions will not stand in a court of law ... !

GB
 
Paddy,

Regs 17th Ed 544.1.2 states:

'The main equipotential bonding connection to any gas, water or other service shall be made as near as practicable to the point of entry of that service into the premises. Where there is an insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer's hard metal piework and before any branch pipework. Where practicable the connection shall be made within 600 mm of the meter outlet union or at the point of entry to the building if the meter is external.'

Memories can be fallible things and suppositions will not stand in a court of law ... !

GB

But there is scope for flexibility.....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Change to regs??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
paddyc3112,
Last reply from
paddyc3112,
Replies
5
Views
1,164

Advert

Back
Top