From what I read it's 25mm incoming tails and a 6mm earth.
No mention of a sub main circuit
No mention of a sub main circuit
It isn't the earthing conductor it is a cpc. The issue is its ability to support PME bonding.
But the bonding issue?[/QUOTE
is it a main BEMCO unit at origin with meter tails fed from DNO fuse to an isolator ?Am I dreaming all this.
Im getting dizzy this thread is going round in circles!!! Op if u want pm me

Clearly not a unique situation. As regards the bonding of services, surely this is done at the intake position for all the flats, as this where the service pipe enterers the property (as a whole) and that is where the bond should be, not in each individual flat?
As the service enters each flat, it may then become an extraneous conductive part and may require bonding or reg 528.3.4 might also apply?
QUOTE]
Scrub that, just read GN8 5.7, (and figure 5.16). I'm also reading in that sizing of bonding conductor (PME supply) is related to the electricity distributor's supply neutral conductor (not the neutral conductor downstream of the cut out on the consumers side, which may have a different csa)