Please confirm landlords cupboard with Ryfield board to meter -meter tails (what size) 60A switch fuse what cable between switch fuse and flat consumer unit ?.This is always going to be a problem when a installation is constructed to a previous addition of BS7671.
 
Interesting conundrum, I haven't any answers just some questions for members.

Clearly not a unique situation. As regards the bonding of services, surely this is done at the intake position for all the flats, as this where the service pipe enterers the property (as a whole) and that is where the bond should be, not in each individual flat?

As the service enters each flat, it may then become an extraneous conductive part and may require bonding or reg 528.3.4 might also apply?

Why would consideration be given to converting to TT, when the property has a perfectly good earthing system (not with standing the bonding issue), and more than probably realistically unachievable?
 
I am thinking the installation was a TNS conversion to TNCS, and the 6mm was fine for the original design. DNO updates to PME and now it's not in accord with BYB.

On the bonding, I think electrical installation starts where the cutout / meter is and the bonding should be where the pipe enters the the location served by that installation, rather than at some other location on the property. But I'm very happy to learn if it's other :)
 
It wouldn't be impossible the services are not bonded at source, I have seen it where they are and where they are not. The services could only serve the dwellings and be totally isolated from any possible common area circuits.
 
Clearly not a unique situation. As regards the bonding of services, surely this is done at the intake position for all the flats, as this where the service pipe enterers the property (as a whole) and that is where the bond should be, not in each individual flat?

As the service enters each flat, it may then become an extraneous conductive part and may require bonding or reg 528.3.4 might also apply?
QUOTE]




Scrub that, just read GN8 5.7, (and figure 5.16). I'm also reading in that sizing of bonding conductor (PME supply) is related to the electricity distributor's supply neutral conductor (not the neutral conductor downstream of the cut out on the consumers side, which may have a different csa)
 
Don't understand why my post forms part of the quote, can't edit either?

Here's what I said anyway, referring to #40

Scrub that, just read GN8 5.7, (and figure 5.16). I'm also reading in that sizing of bonding conductor (PME supply) is related to the electricity distributor's supply neutral conductor (not the neutral conductor downstream of the cut out on the consumers side, which may have a different csa).
 