So what size board does your budget allow? If we round your design load per office down to 20A and say 14 offices/phase you have 20*14=280A per phase.The other problem I have is the budget. It wont facilitate a £1,000 DB Board!
So you wont be using a standard 125A or 250A rated board will you?