Hi all. I’ve got my initial assessment coming up with the niceic and would like to ask a few pointers as regards to my cu change. I have recently changed the cu at a family member’s house for one of the jobs to be assessed on. I have a couple of questions and any help would be much appreciated.
  1. There are no grommets to the back boxes on the light switches. I have tried to install grommets but have found it nearly impossible as the walls are wet plastered and I can’t get in to clean around the edge to put the grommets in place. Is it ok to just note down in the comments on existing installation that no grommets are installed?
  2. When testing the ring I found that testing the r1 r2 with the test plug on my megger that some of the sockets had a high resistance. When I tested at the terminals on the reverse the results were perfect. Do I need to replace these sockets?
  3. I have moved the consumer unit to a more accessible location resulting in extending the cables. I have done this by using a large adaptable box. Each cable has been crimped with the correct size crimp and heat shrink within the adaptable box. The box is then going too boxed around. Will the assessor need to see the adaptable box or can it be plastered in as the crimps are maintenance free?
  4. The latch on the meter cupboard located outside has broken. Is this the supplier’s problem or the consumers. Do I need to correct it? Only asking because it’s an old metal cupboard and not that easy to get hold of a replacement latch.
Thank You
Ashley
 
1, He probably wont be looking in back boxes if you are showing him a CU change, but when i have come across this i have shoved some silicon sealant in the grommet hole.
2, If the results were OK at the terminals, it is OK, chuck your socket tester and buy a new one. Were your ZS's OK?
3, Every termination needs to be accessible, cant quote the exact phrase or reg.
4, Not your problem, but note it on the EIC.

Watch this space, there will be other answers.

Cheers.............Howard
 
Regarding 3, if the results on the terminals are ok, it's fine. Try inserting and removing the tester a few times as a little oxidisation can build up causing a higher resistance reading.
 
Thanks for the reply Howard. I have checked the regs and 526.3 sates " Every connection must be accessible for inspection, testing and maintenance, except for the following: (iv) A joint made by welding, soldering, brazing or an appropriate compression tool" I was under the impression that through crimps where and acceptable form of maintenance free connection and did not need to be accessible. Although I may be mistaken. Thanks again Ash
 