Hi All,
I am tomorrow going to be changing a consumer unit ahead of my Elecsa assessment next week.
Just wanted to check that I'm not missing anything with regards to amendment 3.
I'm going to be using a BG consumer unit supplied with RCBOs.
It has a cut out at back for cable entry and so I am going to pass all cables through that using a grommet strip around the metal edges. Do I need to seal the entry hole? I believe not however I have heard arguments that it needs to be sealed. Passing all cables through the rear entry may require de-rating cables due to grouping however the cables enter the current board (3036's) through the rear. Can i therefore assume ratings are fine?
I am going to attach the consumer unit to the wall using dewalt wall dogs which require no anchor in wall meaning I don't have to worry about plastic wall plugs falling out in the event of a fire.
If the cables are too short (I sincerely hope they won't be) I'll use an adaptable box above the board to mount a din rail to extend wiring. Does this adaptable box need to be non-combustible too? (associated switch gear covers this possibly?)
Thanks in advance
Nick
Went to look at the board change again today and redid all the tests before commencing with the change.
All tests ok except ring final circuit is quirky.
Continuity of ring final:
R1 0.4 ohms
Rn 0.4 ohms
R2 29.8 ohms !!!!
High resistance joint somewhere, taken all the sockets off and checked, couldn't find anything. no spurs in house and only 5 sockets down stairs and 3 sockets upstairs (small house).
Surely there isn't a junction box for such a small house????
I forgot to note the Zs but it was an acceptable value.
Should I go searching for the high resistance joint (lifting boards etc - the fun) or as it has an acceptable Zs is it ok to leave it? (assessor questions)
Thanks all
Just a point how many times have you measured r2 could be an iffy connection on your MFT's leads
if the fault is between the last socket and the CU, as there are not many sockets on the circuit, you could diss. the faulty section (at CU and at socket) and convert to a radial on a 20A MCB. just a though to save cost.
Good luck Nick with your assessment, and you've have been given some good advice by members, especially fault finding!
As regards the fixings for the CU, I take NDG's point, but I do not think that relates to the fixing of CU's more to that of cable supports in escape routes. reg 421.1.201 was all to do with (so I'm told), remove a source of fuel (plastic CU) from the source of a fire. So sealing holes (intumescent), fixings etc don't relate.
As regards using a plastic enclosure above a CU to extend cables, I was advised by Elecsa Tech support a while back (wrongly IMO) that such an enclosure would not comply with the reg, and could not be used in such circumstance. Now that we've had some time, to allow for the dust to settle as it were, I have asked Elecsa for some clarification on the subject. Thought you should perhaps know this before your assessment, just in case. Having said that, when I had my recent assessment, the Elecsa Inspector raised his eyebrows when I told him of the advise given.
Personally, I would use MF joint boxes, in ceiling void above CU, if the cables weren't long enough to terminate in new CU or Ideal in-line splice connectors inside the CU. I would only do that for one or two circuits. Anymore, and I would consider part rewire.
I know faults can be a real pain to find especially when you have been looking for some time!
You say the fault is the last leg or first leg to a S/O from the CU and a CPC fault.
I would be inclined to join L/N at one end and take a reading just to see if the maths matches up with the distance to the CU just in case its a way out reading and the cables run goes elswhere.
Just my opinion as I have come across strange cables runs with no logic in the past!
Good luck with your assessment!
Ok so decided to lift floorboards to satisfy my curiosity. Cable went to an unused and totally forgotten about socket in a cupboard in the hall!
There was a loose connection in that. tightened up and I'm now getting 0.95- 1 ohm.
One would expect it to be 0.7 ohms or so.
My question is, would you continue fault finding to find where the last 0.3 ish ohms are coming from or would you (and my assesssor) agree that as it's close to expected value it's fine?
I would remove the "last" socket and test the Zs on each leg of the ring to see what the readings are like - then consider the options......
The purists will argue you should. But you will have to round to each connection, undo & re-terminate. Your first assessment, your choice. Of course you could argue what you have done thus far has improved the installation, and you determination to locate the fault, might impress your inspector. Perhaps try the former, but you will need to draw the line somewhere, think your Zs' was good?
Pierre or you on the **ss every evening?
Not on the ----, just like the odd glass, nothing serious, it's just people's take on my posts, aint really been on the razz for many a year or two, had my fill of that during my world tour, red wine is my tipple, now I'm retired, but er in doors has got me on a shed building course for OAPs, of course I will be asking advice on how to run a supply to the sheds I build. LOL
Make sure you TT it. Wooden shed, so got to be a wooden earth spike. No, hold on a minute - that wooden work. OK, I'll get me coat. Daz
Not on the ****, just like the odd glass, nothing serious, it's just people's take on my posts, aint really been on the razz for many a year or two, had my fill of that during my world tour, red wine is my tipple, now I'm retired, but er in doors has got me on a shed building course for OAPs, of course I will be asking advice on how to run a supply to the sheds I build. LOL
Now i'd like to expand on this. I too like the odd tipple, of an evening, well most evenings to be honest. Beer mostly but also appreciate a decent red. Seems to be a bit of an undercurrent of frowning upon this sort of thing, can't even turn on my favourite planet rock radio station now without somebody harping on about cutting down: "Do you really need that glass of wine while cooking the dinner". I enjoy a little livener around the 5 O'clock mark myself, bit like yourself by the sounds of it. Do you think it is becoming frowned upon?
I'm fairly certain it's 1.5mm cpc. I can check tomorrow but pretty sure.
Its going to be quite a timely thing to solve where the roughly 0.2Ohm increase is coming from.
Would you guys invest the time to find the cause or would you say 1 ohm is close enough to calculated value and with all other results being good change board?
In your opinion, based on previous assessments, is this something that could fail an assessment?
Depends how on the ball the assessor is, clear the problem and it is one less worry. It wouldn't be something you would outright fail on
What is 0.20 ohms between friends on a conductor that is usually only called upon when something goes wrong. Zs's are good and you have additional RCD protection. Personally I would not worry too much. And yes I would be tempted to record the L and N end to end's as being a little higher and the CPC as a little lower! The assessors are generally pen pushers that like to look at paperwork and not the nitty gritty side of things I have found. That's not having a go at them, it's just the way they are. So, if the paperwork looks about right they are generally happy, and as long as the install is safe. Which I think this one is by the sound of it.
Don't shout at me though if he ain't happy!!
Well done for finding it though mate. I am a little surprised that no one on here asked whether there was a possible long forgotten socket, as it is something a lot of members will have come across, especially on EICRs.
Hi Mid,
My link was a bit off as you say. I have not looked at the full download for a little while but I thought it did a test of standard red/brown wall plugs to hold some of the cable supports up whereby they failed after the fire test. Might be wrong though!
I would think that a CU would hold quite steady in a fire largely due to the various copper conductors stopping it from dropping significantly. But fair play to the OP using a belts and braces approach to keeping it on the wall.
I'd be tempted to record the values as they are seeing as repeating tests and comparing them to recorded values is a usual part of the assessment procedure. I'd rather be explaining an identified anomaly, the action already taken, and the reasons behind not being overly concerned about it, than why values don't match those of the schedule of test results.
I know what you are saying Andy, and yeah OK it's a tiny bit naughty. But cheating L-L up by 0.02 ohms and the CPC down by the same is hardly likely to be picked up on. You will know how values can dance around a bit when testing low impedances.
This install sounds safe to me. It's not like doing a drive by EICR is it.
Totally agree in this specific instance, maybe not in another though.
I know my Elecsa assessor would have picked up on different values as an opportunity for a bonus question such as "Why do you think the values are not as expected ?" or "What could be causing the change in values between measurements ?" But then, most aren't as thorough/bothered as him.
I just had a look at that BRE report and it does use yellow and red plugs to fix some of the supports up. And scan reading it some of these failed. I was responding to Westward originally in relation to the post saying that the plugs would likely hold firm. It was my belief also that they would hold firm, but maybe they won't. So perhaps concrete screws are the way forward.
But that report relates to the installation of electrical cables supports & fixings, and the IET references the report as fire performance of cable supports. Regulation 421.1.201, which specifically makes recommendations about the non combustibility of consumer units and similar switchgear, does not make any specific recommendations on how to fix them to the wall.
Perhaps the 18th edition may have a new note, or 421.1.202 which will tell us to use non combustible fixings. But until then, I don't think we should make that strategic decision IMO.
Thanks for finding & posting the report though.
Hi Guys,
Attached are my forms. Would appreciate it if you could check to see if I've ticked the correct boxes and my results look ok.
One other cause for concern is item 7.7 on the schedule of inspections.
The earthing conductor present before the board change was 6mm and so it needed to be upgraded to at least 10mm (tails are 16mm). I upgraded to 16mm.
I did not realise at the time that the tails and earthing conductor were 3 core.
It was not possible for me to bring the new earthing conductor along the same path as the 3 core cable without a lot of chasing.
I opted to bring the new earthing conductor into the house by a different route aided with trunking and fire clips where needed.
All circuits and tails were chased when installed (some 40 years ago) and entered the old fuse board through the back. I have brought all those cables through the back of the new consumer unit however I could not (without chasing and running the risk of damaging the already installed cabling) bring the new earthing conductor in through the rear.
I have read varying opinions on this with some saying it is ok for the earthing conductor to enter through a separate hole of the consumer unit (with some saying niceic advise that it doesnt apply to meter tails and earthign conductor so long as meter tails L & N enter same hole) and some saying it's not ok and should be noted as a deviation from the regs.
What would you guys do for assessment purposes? Would you enter it as a deviation? Would an assessor accept a deviation like this?
Sincere thanks to you all for the help so far
Hi Nick,
I would not list the main earth coming into the CU by itself as a deviation. I have never heard anyone ever say that it would be. Nor do I understand why it would be. Meter tails should be brought through together on metal enclosures due to possible eddy currents. That is what item 7.7 refers to.
Had a quick look through your cert. Couple of bits I noticed; on schedule of test results polarity is to be ticked. Think you have mistakenly put a megohm figure in mate. Also, as it's all RCBO protected I would expect different values for x1 & x5 tests. Seems to be a lot of 28.8 across the various RCBOs. Also you have not put anything in the "description of installation" box on the first page...I would put new consumer unit and upgrade to main earth and bonding in that box. I would also mention that you carried out remedial works to the RFC CPC due to the end to end value you got.
What are the IR readings? Does that say >2 ?? My test meters highest reading is >299Mohms @500V, which is the value I write down.
And why were some Zs' calculated?
Other than the niggly bits I mention it looks OK with a quick scan.
Hi ndg,
Thanks for scanning over the forms. I too was surprised at all the 28.8s across 3 of the rcbos but they were all tested individually. For lights and heating they were tested at board and for cooker and sockets they were tested at the sockets.
I did indeed miss polarity box, I hope I wouldn't have when I wrote it out as a final copy!
Yes all irs are >2
I picked up on this forum about the main earth needing to come in with the meter tails. regulation 521.5.1. Some say that it doesn't apply to tails, with some saying niceic don't consider the tails with this regulation. quite confused by it all as it's new to me.
OK, fair play re the x1 x5, but test the cooker and sockets at the board to.
Does your meter not go higher than >2Mohms... They normally do.
Maybe I am wrong re the main earth. I thought it was just live conductors only that had to be together or the board slotted. If I am wrong, thankfully I have used the tail glands on all my metal CUs!
South Wales
Consumer Unit Change
Nickj,
Dave OCD,
