Was just trying to say the other method provides correct division of circuits.
and a dual rcd board doesn't?
Was just trying to say the other method provides correct division of circuits.
I don't know about most of you but my 16th board rcd hasn't tripped in over a year. What's this "minimise inconvenience"? It may sounds like you are trying to get more money off the customer.
Yes RCD's are better but when they come down to the same price as a breaker then things may get better.
) in the last 10 years.Well yes it does but not as effectively as separate rcbos.and a dual rcd board doesn't?
Well yes it does but not as effectively as separate rcbos.
The reason I use dual rcd boards is because of cost. I only use separate rcbos if there are limited circuits. Dual rcd boards are not practical where say you may only have 4 or 5 circuits or space is restricted. I chose the best method for the situation and as you can see from my picture that is the only way I scare customersObviously..... But a dual rcd board is cheaper and to the regs.
I do hope you are not trying to scare customers into buying
I would be kinda gutted if I recorded my newly installed dual rcd A3 CU as a departure from the BS7671? Or are we describing something else?N
No not trying to get more money from anyone, use dual rcd boards myself. Was just trying to say the other method provides correct division of circuits. And yes I list this as a Deviation.
A dual rcd board offers minimum compliance for division of circuits and on a new build this would have been considered. Now consider replacing a CU in an existing installation which had no rcd protection and individual mcbs for each circuit which provides complete division. Fit a dual rcd board in its place and this complete division is compromised. I fit them myself 90% of the time and whilst in one respect it is an improvement due the additional protection the downside on existing installations is full division is lost, this is why I note it as a deviation but this is my opinion.I would be kinda gutted if I recorded my newly installed dual rcd A3 CU as a departure from the BS7671? Or are we describing something else?
You beat me to it.To my mind split load boards are acceptable for new builds, but when used as a replacement, frequently they do not comply because inconvenience has been increased rather than minimised.
I mentioned earlier that the installation is improved by giving additional protection but the original division of circuits is compromised.Whilst I would agree with an argument that for example a CU with one RCD protecting 1 RFC circuit & 1 lighting circuit would not comply (with reg 314.1 (i) & (iii)), and perhaps a few other similar examples, I'm struggling with the generalisation that 'mainstream' dual RCD CU's are a departure from BS7671.
The argument that replacing a old rewirable fuseboard, with dual RCD CU will leave it a worse position than it was (considering said reg), ignores the fact that the installation has been improved by the additional protection afforded by the use of RCD's.
Granted, if an existing installation does not have a division of circuits (ground & 1st floor lighting/RFC sockets for example) to spread across two or more RCD's, then RCBO's or combination of the two would have to be considered.
Ok never recorded a departure before, never knowingly anyway! But take your point.It''s to do with compliance with the Regs is all.
The Regs require we minimise inconvenience.
If you change a CU from individually protected circuits to one here multiple circuits are protected by one device, inconvenience has been increased, not minimised.
This is an allowable departure if the degree of safety is equal to that which would be achieved by compliance with the Regs.
As long as your single or dual RCD set up is as safe as individual RCBOs, it can be recorded as a departure.
Doubt many people do, blame the manufacturers for suggesting they are 17th Ed boards.Ok never recorded a departure before, never knowingly anyway! But take your point.