To my mind split load boards are acceptable for new builds, but when used as a replacement, frequently they do not comply because inconvenience has been increased rather than minimised.
I don't really agree. Keeping inconvenience to a minimum is not the same as saying that it must be no more inconvenient than it was before.

Simply put it means consider the consequences of the design. And if you are happy that it is justified then so be it.
 
I don't really agree. Keeping inconvenience to a minimum is not the same as saying that it must be no more inconvenient than it was before.

Simply put it means consider the consequences of the design. And if you are happy that it is justified then so be it.
Don't care about all that keeping inconvenience to a minimum guff.
What I care about is that the Regulations require us to minimise inconvenience.
If you cannot work out that increasing inconvenience is the opposite of minimising inconvenience, then there's not much help for you.
 
Don't really get what everybody is trying to say here.? There are thousands of 16th ed CU's out there with up front RCD main switch, is that one big inconvenience.? RCBO'S, dual split boards and old boards as I mention,have got to be better than old rewire able,with no RCD protection at all.?
 
I
Don't really get what everybody is trying to say here.? There are thousands of 16th ed CU's out there with up front RCD main switch, is that one big inconvenience.? RCBO'S, dual split boards and old boards as I mention,have got to be better than old rewire able,with no RCD protection at all.?
It's all down to ones interpretation of a particular reg dave. But quite frankly I've got more important things to worry about, like where I hide the gin bottles last night?
 
Cracks me up.
Thousands of lighting circuits with no earth, must be right.
Thousands of CPCs just twisted together, must be right.
Thousands of choc blocks above ceilings not in enclosures, must be right.
Just because there's thousands of something, doesn't mean it's right.

As for interpreting the Regs, why?
How about not interpreting them, and just doing what it says?
Can someone explain why 'minimising inconvenience' doesn't actually mean minimising inconvenience?
Is the reason why people interpret the Regs, simply because it's too hard to comply?

After you've finished interpreting 314.1 so that it doesn't mean what is says, how do you deal with 314.2?
How do you interpret 'circuits not being affected by the failure of other circuits'?
Perhaps you just tip ex that bit out?
 
Can someone explain why 'minimising inconvenience' doesn't actually mean minimising inconvenience?
It does mean that. It doesn't state that cost etc. aren't considerations though.

So something can be minimally inconvenient, as appropriate, without going to ideal or most expensive solutions.

Being minimally inconvenient also does not state that if the residual current protection did not previously exist then this cannot cause more than one circuit to disconnect. Against, whilst this may be the best solution it isn't a required solution. These are all considerations for the designer. In my opinion it is you who is reading things into the Regulation which aren't actually contained within it. Although certainly different people may well have differing interpretations as to what is intended by the Regulation.
 
Again, a load of guff.
Please just explain how doing the exact opposite of the requirements of 314.1 can comply?
How can increasing the inconvenience be seen as minimising it?
How can increasing the possibility of unwanted tripping be seen as reducing the possibility?
To top it off, now we are not interpreting the Regulations, but their intentions.

How about just comply with the Regulations rather than spend all this time and effort making excuses, trying to get round them?
 
I think this is down to interpretation on the regulation to be honest and you have to remember that the BS7671 covers industrial and commercial as well as domestic, with regards to inconvenience this would be lost production, down time etc through poor design, something not usually associated to a domestic level, as much as domestic goes I would say if the unit is in a cellar then a split board could mean you lose the cellar lighting if say you have an earth fault on a non-related circuit so we have a situation where you can implement some form of emergency lighting or advise the customer to always have a torch available.
Having half a board tripping is a nuiscance IMHO but not what I would class as an inconvenience, having a section of your factory down and lost production and workers twiddling thumbs is very inconvenient and costly, situation like this are what I suspect the regulation is more aimed at.
 
As for interpreting the Regs, why?
How about not interpreting them, and just doing what it says?
Can someone explain why 'minimising inconvenience' doesn't actually mean minimising inconvenience?
Is the reason why people interpret the Regs, simply because it's too hard to comply?
?

Clearly we are reading this regulation differently, by 'interpreting' slightly differently 'minimizing inconvenience' (incidentally why are they using the American spelling!). Otherwise we would not be having this conversation. If the regs were statuary, lawyers would have a field day. If BS7671 was so clear cut and precise, there wouldn't be half the threads on this forum.

However, it isn't and we do. So I think it's good to have said discussions. :)
 
Hi - this one is a challenge. Having spent the last half hour with Oxford wordybook and its view of what shall, necessary, avoid, minimise and inconvenience mean, I now see Spin's take on 314.1 and 314.2 :)
Is anyone plugged into IET and can get guidance on how the very common domestic split load boards sit with these two regs? Either way, that would be nice.
 
If it is the case fine, I can see myself making a shed load of money altering some CU's I've come across.

Wish IET would issue some guidance, I'm waiting for some on one of their recent regs 421.1.201. Think we've all seen the Elex 15 at Harrogate vid, when a few questions from the audience were met with a 'we seeking guidance on that' :)
 
Don't need to alter anything, unless you incorrectly installed it.

What guidance do you need for that?
Use a metal CU, or a plastic CU in a metal cabinet.
 
Don't need to alter anything, unless you incorrectly installed it.

What guidance do you need for that?
Use a metal CU, or a plastic CU in a metal cabinet.

I wasn't trying to be personnel, but just making a point that I have seen more than a lot of CU's, installed by electricians/companies etc that do not appear to have been installed to reg 314, as to your assessment. Now they may be wrong and you may be right, but they does seem to be some incongruities here.

Non combustible material, ferrous metal being an example, please. There have been quite a few threads querying things like, plastic isolators in meter cupboards, 'what is similar switchgear', plastic enclosures with din rail connectors for CU change etc are just a couple. I have asked my scheme to clarify and have received conflicting responses. At the same show Napit & Elecsa were in a disagreement over 521.11 in domestic properties above a half fire barrier.
 