Consumer unit installed on it's side. | Page 2 | on ElectriciansForums

Discuss Consumer unit installed on it's side. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 18, 2012
Messages
194
Reaction score
39
Location
Leeds
Hi All..thoughts on this please, is it acceptable or failed 'as not installed to manufactures instructions'?

Thanks in advance
[ElectriciansForums.net] Consumer unit installed on it's side.
 
Last edited by a moderator:
One of the new regulations, 536.4.203, states that devices and components that are used in low voltage assemblies (to BS EN 61439) such as consumer units, and distribution boards must only be those that have been declared suitable for that purpose by the manufacturer of the assembly. Or put another way: only use manufacturer approved parts, don’t mix brands of devices or control items.

Taking the above comment possibly to a bit of an extreme, If I have a Hager board and fit Siemens MCB's the quote above would seem the indicate the installation does not conform?
 
As manufacturers guidelines cannot cover 100% of circumstances then sometimes it's down to your call, you have to make the decission as to weather it's safe.
Mounting a DB sideways is NOT dangerous.

sideways (vertically mounted) could indeed be the ‘correct’orientation and everyone else has been doing it wrong for years...
 
Agree that the MCBs are OK this way as they are in a 3-phase DB, but I think having the main switch in any orientation other than down=off is unacceptable as it could hinder isolation in an emergency. I believe the BS defines this but cannot offer a specific reference at the mo. Consider a fire crew working in the dark / smoke...

However DBs with a horizontally acting mainswitch do exist, the small (5 way iirc) 250A Merlin Gerin panelboards have the incoming device connected in the same orientation as the outgoing devices.
Also the old doorman death panelboards have the same arrangement.
 
I believe there is an issue here - essentially BS EN 61439 has that the main switch should operate on - in an upward direction, and it does not in this case, so even if the manufacturer doesn't specifically state anything it ought to be implied.

However I would check with the manufacturer themselves, Hager specifically state that they must be installed in the horizontal plane only, and from memory I have seen it with others as well.

If the manufacturer has stated a direction then it would warrant a C3 to me, if not I don't think there is sufficient justification to argue the point even though it is implied.

Now moving forwards with amd 1 and the 18th I think there are further issues - the principle of the compliant enclosures (BS EN 61439-3) is not just the material (the really, really ought to be metal thing), but that the enclosure should prevent movement of flame forward outwith the enclosure, which implies that the door should also ensure self-closure to enable this.

Now it isn't directly in BS EN 61439-3, but BEAMA have stated in their technical bulletin that the standard describes effective control of flame by having a case, a cover and a door in place.

... And that if the door may be left open, then in effect it isn't compliant.

Obviously this installation predates this, but is the case for anything since 2016

(and of course this metal and so on restriction only applies to homes, not commercial etc)
 

Reply to Consumer unit installed on it's side. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
211
Google says that North Walney is in the Lake District? Have we moved the wall :)
Replies
6
Views
517
  • Question
Same as above, if the property is old which your posts suggests i would definetley get an EICR first incase to see what conditon the installation...
Replies
2
Views
400
  • Question
I've a (large, with private water treatment, ground source heating, workshops....) house I built in Devon many years ago - by the 'add it all up'...
Replies
19
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks