One of the new regulations, 536.4.203, states that devices and components that are used in low voltage assemblies (to BS EN 61439) such as consumer units, and distribution boards must only be those that have been declared suitable for that purpose by the manufacturer of the assembly. Or put another way: only use manufacturer approved parts, don’t mix brands of devices or control items.


Each manufacturer of electrical switchgear designs and tests its own products for use in combination with each other, not with other brands. So if someone were to use a mixture of brands they would be creating an untested assembly and untested assemblies aren’t backed by manufacturer guarantees.


Obviously, no manufacturer can guarantee an installation that hasn’t been completed in line with the manufacturer's installation instructions. But that doesn’t mean that manufacturers won’t permit control items to be added to an assembly. Electrium, for example, offers a custom build facility and will design & build factory built assemblies that will carry a manufacturer guarantee, even if the assembly includes non Electrium products.


Readers should be aware that the notes relative to 536.4.203 state that if the assembly deviates from the original manufacturers' instructions then the person introducing that deviation becomes the manufacturer. So if you have an installation that requires non-standard arrangements talk to the manufacturer about how to provide this in a compliant manner.


Using unapproved parts will invalidate manufacturer guarantees and may result in an unsafe installation.
so where do it says you can not turn the C/U on its side and what about three phase boards .
One of the new regulations, 536.4.203, states that devices and components that are used in low voltage assemblies (to BS EN 61439) such as consumer units, and distribution boards must only be those that have been declared suitable for that purpose by the manufacturer of the assembly. Or put another way: only use manufacturer approved parts, don’t mix brands of devices or control items.


Each manufacturer of electrical switchgear designs and tests its own products for use in combination with each other, not with other brands. So if someone were to use a mixture of brands they would be creating an untested assembly and untested assemblies aren’t backed by manufacturer guarantees.


Obviously, no manufacturer can guarantee an installation that hasn’t been completed in line with the manufacturer's installation instructions. But that doesn’t mean that manufacturers won’t permit control items to be added to an assembly. Electrium, for example, offers a custom build facility and will design & build factory built assemblies that will carry a manufacturer guarantee, even if the assembly includes non Electrium products.


Readers should be aware that the notes relative to 536.4.203 state that if the assembly deviates from the original manufacturers' instructions then the person introducing that deviation becomes the manufacturer. So if you have an installation that requires non-standard arrangements talk to the manufacturer about how to provide this in a compliant manner.


Using unapproved parts will invalidate manufacturer guarantees and may result in an unsafe installation.
so where do it says you can not turn the C/U on its side and what about three phase boards .
It doesn't say in the regs....but if the manufacturers instructions say you cant then you cant.......follow manufacturers instructions......easy
 
One of the new regulations, 536.4.203, states that devices and components that are used in low voltage assemblies (to BS EN 61439) such as consumer units, and distribution boards must only be those that have been declared suitable for that purpose by the manufacturer of the assembly. Or put another way: only use manufacturer approved parts, don’t mix brands of devices or control items.

Taking the above comment possibly to a bit of an extreme, If I have a Hager board and fit Siemens MCB's the quote above would seem the indicate the installation does not conform?
 
As manufacturers guidelines cannot cover 100% of circumstances then sometimes it's down to your call, you have to make the decission as to weather it's safe.
Mounting a DB sideways is NOT dangerous.
 
considering thet in Australia you mount them upside down........
 
As manufacturers guidelines cannot cover 100% of circumstances then sometimes it's down to your call, you have to make the decission as to weather it's safe.
Mounting a DB sideways is NOT dangerous.

sideways (vertically mounted) could indeed be the ‘correct’orientation and everyone else has been doing it wrong for years...
 
they're all the same lying down. Oops, that was meant to go in the preferences column of the eharmony dating site. :p :p :p
 
Agree that the MCBs are OK this way as they are in a 3-phase DB, but I think having the main switch in any orientation other than down=off is unacceptable as it could hinder isolation in an emergency. I believe the BS defines this but cannot offer a specific reference at the mo. Consider a fire crew working in the dark / smoke...

However DBs with a horizontally acting mainswitch do exist, the small (5 way iirc) 250A Merlin Gerin panelboards have the incoming device connected in the same orientation as the outgoing devices.
Also the old doorman death panelboards have the same arrangement.
 
I believe there is an issue here - essentially BS EN 61439 has that the main switch should operate on - in an upward direction, and it does not in this case, so even if the manufacturer doesn't specifically state anything it ought to be implied.

However I would check with the manufacturer themselves, Hager specifically state that they must be installed in the horizontal plane only, and from memory I have seen it with others as well.

If the manufacturer has stated a direction then it would warrant a C3 to me, if not I don't think there is sufficient justification to argue the point even though it is implied.

Now moving forwards with amd 1 and the 18th I think there are further issues - the principle of the compliant enclosures (BS EN 61439-3) is not just the material (the really, really ought to be metal thing), but that the enclosure should prevent movement of flame forward outwith the enclosure, which implies that the door should also ensure self-closure to enable this.

Now it isn't directly in BS EN 61439-3, but BEAMA have stated in their technical bulletin that the standard describes effective control of flame by having a case, a cover and a door in place.

... And that if the door may be left open, then in effect it isn't compliant.

Obviously this installation predates this, but is the case for anything since 2016

(and of course this metal and so on restriction only applies to homes, not commercial etc)
 

Reply to Consumer unit installed on it's side. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
246
Hi. Can a horizontal 200A consumer unit be fitted vertically, or is there a vertical configuration? I have a 350mm wide space...thanks.
Replies
19
Views
817
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
739
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
I want to know if my consumer unit (together with the digital meter) which is in a special metal container let into an outside wall near the...
Replies
2
Views
377

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock