Hi, we have been asked to relocate a consumer unit however the meter cupboard will be on an outside wall 7m away from the consumer unit, the main switch is under 80amp, im just wanting some opinions on the way to overcome this, am I right in thinking I could run 16mm swa from the consumer unit, cleated to an outside wall, running to an adaptable weatherproof box situated next to the meter cupboard, then using Henley connector blocks, i could connect the swa to the tails coming from the meter box.
 
That makes things a lot easier then..
What is going where the old cu is located?
Can the isolator go there?
Its a temporary thing at the moment, the meter is being moved friday but for now until a few months down the line the cu is staying where it is, then eventually it will moved behind the meter cupboard, so really for now I need to connect the exsisting cu to the new mrter cupboard
 
The meter boxes have knockouts in the bottom that can be reinstated later on..
I would come out of the bottom in trunking and then go bottom entry into an enclosure with the isolator inside.
We’re supposed to use designated entry points in the meter boxes
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
South wales

Thread Information

Title
Consumer unit replacement
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
Mikey10695,
Last reply from
Charlie_,
Replies
27
Views
3,499

Advert

Back
Top