Hi,
Just after your thoughts on the following-
I am running a 25mm armoured from a KLM switch fuse to a consumer unit under the stairs in a domestic property. I intend to gland into a joint box and take 6181Y meter tails to the consumer unit. Under the 18th a edition the consumer unit needs to be metal but is there anything preventing me used a plastic adaptable box under the stairs instead of a metal one?
 
If you do use a plastic box, make sure it is strong enough not to crack or disintigrate when you gland the SWA into it, and the SWA doesn't want to sit exactly where you need it to.
 
I’d make the gland off, fit it to the box and THEN screw it to the wall… rather than trying to bend the cable to an already fixed box… that’s when you get the stress on the plastic.
 
I’d make the gland off, fit it to the box and THEN screw it to the wall… rather than trying to bend the cable to an already fixed box… that’s when you get the stress on the plastic.
Yes, good point. I'm limited for space so it will boil down to what the best size box is available be it metal or plastic. I agree with the other comments that metal is the preferred one for 25mm swa.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Consumer unit under stairs
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
sparky24,
Last reply from
WallaceP,
Replies
8
Views
3,266

Advert

Back
Top