The adequacy of the existing installation is thereforerequired to be Assessed in Three - Areas . ◄◄
i) Existing equipment – including that of the supply : whichmay have to carry Increased Loads .
it is necessary to establish that the rating &condition of all appropriate equipment within an installation – Such asOvercurrent protective devices . Final & Distribution circuit conductors .Switchgear & Distribution boards . is capable of supporting the planned Addition or Alteration . The condition of the existingequipment should be Assessed for its ability tocarry any Increased Load . & where appropriate . Inrush & Startingcurrents . & for Defects . Omissions . Damage . & minor deterioration . any inadequaciesin the Existing Installation that would resultin a reduced level of safety in the new work – That is a level of safety lessthan afforded by compliance with BS-7671 – must be corrected before the newwork is put into service .
( The electricity distributorsequipment may have to carry Additional Load - & Inrush & Startingcurrents . & its suitability & condition must be Assessed . The distributor should be Assessed . The distributor should beRequested to upgrade the supply . ( WhereRequired )
ii) Earthing & Bonding arrangements .
Assessing the adequacy & suitability of the Existing Earthing & Bondingarrangements .
• Establishingthe suitability of means of Earthing in respect of its Type . such as a ( PME ) Earthingterminal or an earth rod . & condition – is it Corrodedor Damaged or Inaccessible. ??????
“ Verification “ of themeans of Earthing by determination of the external earth fault loop impedance (Ze ) See regulation 313.1. if ( Ze ) is determinedby enquiry or calculation. it is necessary also to obtain a Measured Valueto verify that the intended means of earthing is both present & of theexpected value .
( Determination of external earthfault loop impedance at the Origin of the Installation )
• Ascertaining that the Earthingconductor is of Adequate Cross-sectional area ( C.S.A.)
Establishing . determining or confirming the presence &adequacy of circuit protective conductors for both the final circuit(s) &any distribution circuit(s) forming part of the Additionor Alteration .
Where the protective measure against electric shock isAutomatic Disconnection of supply ( ADS ) the adequacy of the exitng bondingmust be established . it is an essential requirement for safety that mainprotective bonding is provided
iii) Certain Additional considerations .
Additional considerations relating to the existing installation orany effects that the Addition or Alteration may have upon it . such as those mentioned inregulations ( 131.8.) but are covered by other requirements of BS-7671:2008 .& are therefore Applicable .
Grouping Effects .
The Rating of all Cables in the Wiring System. both existing & proposed additional cables . must be assessed to take accountof any additional Heat Generated by the larger grouping . & be derated asnecessary . if the existing cables would not be adequate when derated . Then oneoption would be to install the new cables separately from the existing groups
i) Existing equipment – including that of the supply : whichmay have to carry Increased Loads .
it is necessary to establish that the rating &condition of all appropriate equipment within an installation – Such asOvercurrent protective devices . Final & Distribution circuit conductors .Switchgear & Distribution boards . is capable of supporting the planned Addition or Alteration . The condition of the existingequipment should be Assessed for its ability tocarry any Increased Load . & where appropriate . Inrush & Startingcurrents . & for Defects . Omissions . Damage . & minor deterioration . any inadequaciesin the Existing Installation that would resultin a reduced level of safety in the new work – That is a level of safety lessthan afforded by compliance with BS-7671 – must be corrected before the newwork is put into service .
( The electricity distributorsequipment may have to carry Additional Load - & Inrush & Startingcurrents . & its suitability & condition must be Assessed . The distributor should be Assessed . The distributor should beRequested to upgrade the supply . ( WhereRequired )
ii) Earthing & Bonding arrangements .
Assessing the adequacy & suitability of the Existing Earthing & Bondingarrangements .
• Establishingthe suitability of means of Earthing in respect of its Type . such as a ( PME ) Earthingterminal or an earth rod . & condition – is it Corrodedor Damaged or Inaccessible. ??????
“ Verification “ of themeans of Earthing by determination of the external earth fault loop impedance (Ze ) See regulation 313.1. if ( Ze ) is determinedby enquiry or calculation. it is necessary also to obtain a Measured Valueto verify that the intended means of earthing is both present & of theexpected value .
( Determination of external earthfault loop impedance at the Origin of the Installation )
• Ascertaining that the Earthingconductor is of Adequate Cross-sectional area ( C.S.A.)
Establishing . determining or confirming the presence &adequacy of circuit protective conductors for both the final circuit(s) &any distribution circuit(s) forming part of the Additionor Alteration .
Where the protective measure against electric shock isAutomatic Disconnection of supply ( ADS ) the adequacy of the exitng bondingmust be established . it is an essential requirement for safety that mainprotective bonding is provided
iii) Certain Additional considerations .
Additional considerations relating to the existing installation orany effects that the Addition or Alteration may have upon it . such as those mentioned inregulations ( 131.8.) but are covered by other requirements of BS-7671:2008 .& are therefore Applicable .
Grouping Effects .
The Rating of all Cables in the Wiring System. both existing & proposed additional cables . must be assessed to take accountof any additional Heat Generated by the larger grouping . & be derated asnecessary . if the existing cables would not be adequate when derated . Then oneoption would be to install the new cables separately from the existing groups