Sequenceof Tests : 2392-10
:earmuffs:
Point to Note )- The Danger is compounded if Tests are NOT carried out in the CorrectSequence .
Why???
SomeTests require the Supply to be On . -&-s . will come up on this Matter .
BS-7671.States the Order weshould carry out the Tests .
Approved Document P . Electrical Safety – Dwellings .
Note : Lackof Knowledge of a Regulation is No Defence in Law .
Electricians’ Guide to the Building Regulations
ApprovedDocument P .
p/16)- ( P1 ) Design Installation .
Reasonableprovision shall be made in the Design & Installation of electrical installationin order to protect person operating . maintaining or altering the installationfrom Fire or Injury .
BuildingRegulations - ( BR ) p/7 .
ApprovedDocuments are intended to prove guidance for some of the more common buildingsituations . However there may well be alternative ways of achieving compliancewith the requirements .
Thusthere is No Obligation to adopt any particular solution contained in an ApprovedDocument if you prefer to meetthe relevant requirement in some other way .
Asfor -&-s )- ADwelling is a place of Work when work is Undertaken . p/9
This( ACT ◄◄◄) Empowers the “ SECRETARYof STATE “ ( -&-s) to make Regulations . Etc.
:39:
2392-10: Just an Insight . to some Testingmethods :waving:
EarthLoop Impedance ( Zs )
612.11. Prospective Fault Current . ( PFC )
Whendesigning an Installation . 2392-10 – it is theDesigner’s ( You) responsibility to ensure that . Should a Line –to Earth Fault develop .
TheProtective Device will operate safety & withinthe time Specified by BS-7671 .
Itis ” NOT “ until the Installation is complete& “ Live “ that the calculations can be “ Checked “ ( Energized )
What -&-s are looking for)- it is Necessary therefore to “ Determine “the Earth Fault Loop Impedance ( Zs )
Atthe “ Furthest Point “ in each circuit & to “ Compare the Reading “ obtained with calculated valuesTabulated in BS-7671 or the O.S.G.
2392-10)- With an Earth Loop Impedance Tester ◄◄ ( For the purpose of -&-s ) You will beUsing a Megger multifunction tester –MFT 1552 ??
Thevalue of Earth Fault Loop Impedance ( Zs ) may be“ Determined by ?
)- Direct ►Measurement of ( Zs ) at the furthestpoint in the Circuit .
MaximumPermissible Measured Earth Fault LoopImpedance .
“ Wording“ Note .
O.S.G.– p/103 )- Table 2D gives the Maximum Measured ◄( Zs ) for circuits protected by MCBs to BS-EN 60898 & BS-EN 61009-1 ( At Ambient Temperature ) ◄ ( 0.1 to 5s . disconnectiontimes )
Thetabulated values apply only when the Nominal Voltage to Earth ( Uo ) is 230V . scenario only . PFC – 230 /Uo ÷ 1.16 = 198A . – ( B – 32A – 1.16 )
(PFC ) - Although the Designer can calculate this in theory .
Regulation41.3. p/49 )- Maximum ◄ Earth Fault Impedance( Zs ) Compliance with ( 0.4s – 5s )
)- Direct ►Measurement of ( Ze ) for-&-s ( At the Origin of the Circuit ) &adding value of ( R1 + R2) measured during ( Continuity Tests )
ElectricitySupplier )- Obtaining the value of ( Ze ) from the DNO. & adding to this value of ( R1 + R2 ) … Zs = Ze + ( R1+ R2 )
(Ze ) this is a Live Test . ( So –Ze is the Loop Impedance value External to the Source of the Circuit(s) Supply)
(Ze ) Live at the Incoming Terminals ) -&-s are looking for ( Safe Isolation ) You are only testing the Top of the MainsTails Live . The bottom has been ( Safe Isolation)
► DirectMeasurement of ( Zs)
Earth Fault Loop Impedance isachieved by use of an Earth Fault Impedance Tester . This Instrument operatesfrom the “ Main Supply “ & therefore canonly be used on a “ Live Installation “ ( Care must beTaken Here )
Testersare connected directly to the “ Furthest Point “ of the Circuit – it must be Noted that Parallel Paths may be present whichwill affect the True Circuits Earth Loop Impedance Reading .
► Measurement of ( Ze )
Thevalue of ( Ze ) can be Measured using an Earth Fault Loop Impedance Test at the“ ORIGIN “ of the Installation .
Megger multi function tester – MFT 1552 ??
Theinstrument is connected using approved Leads between the “ Line “ terminal of the Supply & the means ofEarthing . ( with the Main switch closed OFF /Isolated )
2392-10)- -&-s . In order to remove the possibility of Parallel Paths . The meansof Earthing must be Disconnected from the Main Protective Bonding conductors -&-sfor the duration of the TEST.
► Measurement of Prospective Fault Current ( PFC &PSCC )
ThisTest is made with an Earth Fault Loop Impedance Tester set to Amps
TheProspective Fault Current . Which is how much current will flow in the event ofa Fault . is divided into two-parts .
ProspectiveEarth Fault Current ( Line to Earth Fault )
The( PFC ) test is measured at the furthest point or can be calculated using the (Zs ) value
The( PFC - Test ) is made at the Origin of the Installation & its value .Obtained in ( kA ) is then compared to the Fault Current ratings of theProtective Devices .
(PFC ) & ( PSCC ) tests are actually both carried out at the relevant point& the Higher of the Two-Values is recorded in particulars of the Origin ofthe Installation .
2392-10.
Insulation Résistance . Tests should be made on a Dead Test .
Competenceof the Inspector .
A finalconsideration when carrying out Inspection & Tests is the competence of theInspector . ( it is the Responsibility of the Inspector to )
132.1– ( i ) • Ensure no Danger occurs to People . Property & Livestock .
• Confirmthat Test & Inspection results comply with the requirements of BS-7671:2008. & the designers requirements .
• Expressan Opinion as to the condition of the Installation & recommend remedialwork(s) .
• Makeimmediate recommendations . in the event of a dangerous situation . to the Client to Isolate the Defective Part(s) -&-s
InspectionRequirements : 2392-10
Requirementsfor both Basic & FaultProtection .
ElectricalSeparation . Which means NO ElectricalConnection between the SELV Circuit & HIGHER VOLTAGE SYSTEMS .
2392-101: The Customer .
FollowingInitial Verification . BS-7671 requires that an Electrical InstallationCertificate .
Togetherwith a Schedule of Test Results & an Inspection Schedule .
Shouldbe given to the person ordering the Work .
Initial Verification 632.1. ..2392-10 Exam ◄◄ . -&-s Should be given to theperson ordering the Work
:waving:
Unlessthis has be Done “ The Regulations have Not been MET.
Calculation – gives you theFigure that it should be .
Measurement – give you theFigure that it is .
Where an Earth Electrode is to be used considerationmust be given to the Earth Electrode .
Inmost cases . we accept that the Electrode Résistance must be no Greater than ( 200Ω )
Wherean Electrode is used for any RCD with a rating Greater than ( 200mA ) theformula ( Ra ≤ 50 / I∆n ) is applied .
Wherea ( 300mA ) RCD is to be used for FireProtection . ( 50 ÷ 0.3 = 167Ω )
Thiswould be the maximum permitted résistance of the Electrode & the protectiveconductor connecting it to any Exposed Conductive Parts .
Table11A ) Rating Factor(s) for triple harmonic currents in four-core &five-core cables
:6:
Balancedthree phase load is to be installed which has adesign current of ( 26A )
Manufacturerhas stated that the equipment being installed has a harmonic distortion of ( 30% )
Therating factor of ( 0.86 ) Table 11A – BS-7671can be applied to calculate the minimum permissible rating for the conductor ( 26A ÷ 0.86 = 30.23A )
Table11A – BS-7671 . p/356 .
Therating factor of ( 0.86 ) can be used only forequipment with Harmonic Distortion of up to ( 33%) p/356
Abovethat the calculation has to include the percentage distortion .
Harmonicdistortion for the equipment ( 45% ) …. 26A x 45% ÷ 100 x ( 3) = 35.14 .
:nopity:
3) it is a three-phase supply .
three-phasecircuit(s) . triple harmonic neutral currents [ 3[SUP]rd[/SUP] . 9[SUP]th[/SUP] . 15[SUP]th[/SUP] . ] etc
causethe largest concern as they add instead of cancelling . since they aremultiples of three times the – Fundamental power frequency & are spacedapart by ( 120 Electricaldegrees )
basedon the fundamental frequency . triple harmonic currents of each phase are inphase with each other & so add in the neutralcircuit . Under the worst case conditions . the neutral current can be ( 1.73 times ) the phase current .
greatdeal of electronic equipment requires what is known as ( Clean Power Earth ) unfortunately .
itis the high-frequency harmonic currents due to the switch mode power supplies whichcause the distortions in the first place .
thesedistortions can also have an adverse effect on ( the Earthingsystem of Installation(s) particular lot of PCs in use . These distortionsare often the cause of noise bars on PCs . monitors. in these cases consideration must be given to providing a copper Earth mat which is connected to a very good Earth& connecting each piece of ( IT equipment separately )
Designing:
:53:
Forall cables over 16.0mm[SUP]2[/SUP]there are Three-values given for Volt –drop [ r . x . & y . ]
Thereis a complex calculation in which these values can be used to calculate areduced voltage drop within a cable depending on the conductor temperature .
Anyoneusing cables greater than 16.0mm[SUP]2[/SUP] would be to use the Value ( r) in the voltage drop calculation as this will always give a value which is onthe right side of SAFE
Apprentices. RCDs
TheTerm “ Additional Protection “ is usedthroughout the “ 17[SUP]th[/SUP] Edition “ The use of RCDsare recognised as a means of providing additional protection in the event ofFailure of the provision for “ Basic Protection “
Asan “ Additional Means ” of “ Fault Protection “& to protect againstCarelessness by USERS.
Fromyou point of View ??
Ifan RCD is Used to provide “ Additional Protection“ it then meet the requirements of Regulation 415.1.1.Thatis . The RCD must have a rated Residual Operating Current not Exceeding ( 30mA ) & an operating time NOT Exceeding ( 40mS ) at ( 5 x therated current ) . Yeah
Thisone you will get in 2392-10 Exams . “ AdditionalProtection “ :earmuffs:
Therequirements of Regulation 314.1.. Division of Installation . :6:
Needto be taken into account when designing & installing the circuit protectivearrangements . 314.1. State(s) that Every Installationshall be divided into circuits as necessary:
i)Avoid hazards & minimize inconvenience in the event of a Fault .
iii)Take account of Danger that may arise from the Failure of a Single Circuitsuch as a Lighting Circuit .
iv)Reduce the possibility of Unwanted Tripping of RCDsdue to excessive protective conductor current produced by equipment in Normal Operation .
Apprentices )- This means a Single RCD cannot be Used toProtect the Whole Installation . As in the Event of a Fault . Power will be Lostto all Circuit potentiallycausing Hazards . ( Inconvenience & Danger )
So)- Therefore Multiple Devices should be Installed to protect the Outgoingcircuits & should also be ( SPLITacross the RCD )
Apprentices. RCDs :39:
Scenario)- Shower – PowerCircuit . ( Remember – No Diversity on a Shower . 100% )
(RCBO ) 40A upto 50A
RCBO. Type ( B ) SP / 50A – 30mA – ( 6kA ) ….. 50A . is Breaking Capacity / 30mA . isFault Prospective Current . ( it meets the criteria of the 17[SUP]th[/SUP] Edition – ADS)
IndividualProtection for Designated ( Single ) Circuit . ?
(RCBO ) is a ( MCB / RCD ) Functions ofprotection against ( Overload & / or Short Circuit ) Regulations . Definitions – p/29
( MCB) from same Origin ( Overcurrent )
50A- B . Type – This means it will tripbetween ( 3 & 5) time Full Load Current
B . Type– is Used on Domestic Installation(s)
Asa Designer . the ( RCBO is about £ 50 + Vat )
Asa Designer . the ( MCB is about £ 3 pounds + Vat )
Asa Designer . It all comes down to COST ./ Client
So the Designer may not have the last say on this Matter .
Designing )- Trunking : Calculations.
:6:
Trunkingcontains ( 5 – Three-phase & 3 – Single-phase Circuits )
Equivalentnumber of Single Circuits .
5x 1.5 = 7.5.
7.5+ 3 = 10.5 . in this case a rating factor of ( 0.51) could be Used ( 4C1 )
Equivalentnumber of Three-phase circuits .
3x 0.666 = 1.998 – round up ( 2 )
2+ 5 = 7 )- in this case a rating factor of ( 0.54) could be used ( 4C1 )
Whencalculating the cable size use the Three-phase factor for Three-phase circuits. In this case ( 0.54 )
&Single-phase factor for Single-phase circuits . in this case ( 0.51 )
Designing )- Trunking : Calculations. Part ( 5)
Designing )- part ( 4 )
:6:
Ambienttemperature factor ( Ca ) = 0.87
Groupingfactor ( Cg ) = 0.7
Tabulatedcurrent rating of the cable is ( 24A )
Asthe circuit is in Conduit at ( 40°C ) &grouped with two-other circuits both rating factors must be Applied .
24 x 0.87x 0.7 = 14.61A
Asyou can see . This now reduces the current-carrying capacity to ( 14.61A ) Thisis due to the likely build up of temperature in the cable from being at agreater Ambient temperature ( 30°C ) & theimported Heat from the OtherCables .
Whereall the rating factors do not affect the cable(s) . at the same time only the Worst case needs to be Applied – in this case ( Cg – 0.7 ) in other words .
Ifthe conduit passes through an Environment at ( 40°C ) withonly one cable in & then Enters another roomwhich has a temperature of ( 30°C ) but picksup another two circuits in the room . Only the Worst case needs to be Appliedto your cable . This would be ( Cg – 0.7 )
Insome installation(s) . Three-&Single-phase circuit(s)will be contained in the same Enclosure .
Table. ( 4C1 ) only provides factors for ( Uniform Groups of Cables) . if all of the cables are Three-phase then each Three-phase circuit iscounted as ( One Circuit )
Thefactors from table can be used just as they can for ( Single-phase-circuit(s)This is not the case where there are ( Single-&Three-phase circuit(s) mixed together . & slightly differentapproach to ( Grouping ) has to be taken .
Toestimate the grouping factors for Three-phase circuit(s) in a containmentsystem having mixed groups we must ( Multiply theNumber ) of Three-phase circuit(s) by ( 1.5) then add this number to the number of ( Singlecircuits ) This will give us a figure to USEwith table ( 4C1 )
Estimatingthe grouping factor for ( Single-phase circuits) in a mixed containment system . We must ( Multiplythe number of Single-phase circuits by 0.666 ) & then add this to the number of ( Three-phase circuit(s)
Designing )- part ( 3 )
:6:
2.5mm[SUP]2[/SUP] cable can carry ( 24A )before any ( Correction Factors ) are applied .To calculate the amount of current which the cable can carry before it needs tobe counted as ( A Circuit ) as a circuit in ourgrouping calculation the following formula can be Used
24 x 0.3 x 0.7 = 5.04A )
24 )- is the rating factor ofthe cable from ( column 4 ) table ( 4D1A ) ( 0.3 ) is the multiplier for ( 30%) & ( 0.7) is the grouping factor / Example 2 -
Usingthis calculation shows us that the ( 2.5mm[SUP]2 [/SUP])cable was only carrying ( 5.04A ) we could discount it from our groupingcalculation . for the remaining circuits only a grouping factor for two circuits( 0.8 ) need applied .
Theimportant thing to remember is that for a cable to be discounted for groupingit must only be carrying ( 30% ) of its capacity with the grouping factor forall of the circuits applied . Hence in our example the grouping factor forThree-phase circuits was applied to the ( 2.5mm[SUP]2 [/SUP])cable which has been discounted in the calculation .
Ifwe now look at examples ( 1 & 2 ) again . it is possible that the cable beinstalled in a conduit with two-other-circuits & the Ambient Temperature ofthe Area where the conduit is installed (40°C ) in this case . both correction factorsmust be Applied to the circuit to be installed .
Thiswould result in a further reduction of Current-Carrying Capacity for the circuit .