2392-10:- “ Consumer Controlgear “ 530.3.4. :speechless:

ForInstallation with a 230V single-phase supplyrated up to 100A that are under the control of ( Ordinary Persons) should either .

• Comply with BS-EN 60439-3 & Regulation 432.1. of BS-7671.
• Be a Consumer Unit – incorporating components complyingwith BS-EN 60439-3


 
Regulation Chapter 532 . :- Devices for Protectionagainst the Risk of Fire . :whatchutalkingabout

532.1.Where in accordance with the requirement of Regulation 422.3.9. it is necessaryto limit the Consequence of ( Fault Currents )in wiring system from the point of view of ( Fire Risk ) THE Circuitshall be either .

i)Protected by an RCD complying with Regulation 531.2. for ( Fault Protection ) &
- The RCD shall be installed at the ( Origin of the Circuit ) to be Protected . &
- TheRCD shall Switch all Live Conductors . &
-The rated Residual Operating Current of the RCDshall Not Exceed ( 300mA) ETC .









 
Chapter537 . Isolation & Switching .

Isolation– ( 537.2.
Switchingoff for Mechanical Maintenance - ( 537.3.
EmergencySwitching - ( 537.4 .
FunctionalSwitching - ( 537.5.

Fire-fighter’s Switches – ( 537.6 . :speechless:

A Fire-fighter’sswitch shall be provided in the Low Voltage circuit supplying :

i)( Exterior ◄ ) electrical installationsoperating at a Voltage Exceeding Low Voltage . &

ii)( Interior ◄ ) Discharge lighting installations operating ata Voltage ( ExceedingLow Voltage )

(Temporary Installation ) Fire-fighter’s Switches – ( 537.6.1.

Forthe purpose of this regulation . An installation in a CoveredMarket . Arcadeor Shopping Mall is considered to be an (Exterior Installation )
• A Temporary Installation in a Permanent Building used for Exhibitions isconsidered ( NOT to be an Exterior Installation )



 
“ Isolation“ :icon14:

Itemsto be Considered in Relation to “ Isolation “ devices.

• Number of poles to be “ Isolated“
• “ Isolation “ of groups &inconvenience .
• Devices designed and / orinstalled to prevent Unintentional or Inadvertent closure .
• “ Isolation “ devices to beClearly Indentified and Indicate the Installation or Circuit it Isolates .









 
Isolationrequirements for ( TN-S ) Systems .

Single-phase. L ≈ N - Circuit Protective Conductor .

Three-phase. L1 . L2 . L3. ≈ N . - Circuit ProtectiveConductor .

 
Emergency Switching :icon14:

Whatare the requirements for Emergency Switching in relation . to

• Full Load Current .
• Hand – held devices .
• Identification of Emergency Switching devices .
• Positioning & Accessibility .
• Positioning & Identification .
• Further Danger .








 
Firefighters Switch :

A Fire-fighter’s Switch is a Device intended for Use by Fire Service . ( Although ) NotExclusively SO :speechless:

It’spurpose is to ( De-energise ) designated parts of an Installation . That operateat a voltage in ( Excess of Low Voltage ) Neon Lighting .
 
2392-10: :speechless:

542: Earthing Arrangements .

542.1.General Requirements .
542.1.1.The Main Earthing Terminal . Etc
542.1.2. TN-S .
542.1.3. TN-C-S .
542.1.4. TT or IT .

Chapter54 . p/124
EarthingArrangements & Protective Conductors .

542- Earthing Arrangements . p/126
543- Protective Conductors . p/128
544- Protective Bonding Conductors . p/134 .

ProtectiveConductors .
Areconductors provided for the purposes of Safety . for some measures of Protection Electric Shock . Reg - p/27

Look– fig 2.1 / p32 . Earthing & Protective conductor .

 
2392-10:

-&-s . Q ) How many Types of EarthingSystem are recognised by BS-7671:2008 . :icon14:

A) 312.3.1. p/38 :- Types of System are . [ TN-C : TN-S : TN-C-S : TT : IT :
 
2392-10:

TheEarth Fault Loop Impedance ( Zs ) for a Consumer’sCircuit is determined by ? :icon14:

(R1 + R2 ) + Ze

Part 2 Definitions - P/36 :
 
TheProspective Short Circuit Current at the Origin of the Consumer’s Installationmust be taken into account when ??
Selectingthe type of Overcurrent Protective Device to be installed .

Wherepracticable Main Protective Bonding Conductor . to the Gas services in abuilding should be made within .
[600mm of the Meter on the Consumer Side ] :speechless:

O.S.G.P/27 (- Main Protective Bonding Conductors are required to connect the followingMetallic Parts to the ( Main Earthing Terminal) 411.3.1.2.
Extraneous-conductive-part : A Conductive part such as a Metal Pipe . ( LIBLE )to introduce Earth Potential into the Building.

MainProtective Bonding Conductor is the Electrical Interconnection between the MainEarthing Terminal & the incoming Metallic Services : Water / Gas .

TN-C-S. Earthing arrangements .

Regulations544.1.1. p/134 . & Table 54.8 / p134

IETwiring regulations – 17[SUP]th[/SUP] Edition . The required size of the Main Bonding Conductor is ( 10.0mm[SUP]2 [/SUP] ) for supplieswith a Neutral Conductor of ( 35.0mm[SUP]2 [/SUP] ) or Less

Becauseof this You will be required to use ( 10.0mm[SUP]2 [/SUP] ) Single Core Earth Cable toconnect both the Incoming ( Water pipe ) & the Incoming ( Gas pipe ) to theMain Earthing Terminal inside the Consumer Unit . ( CU )

 
I've skimmed through the last few pages, mostly initially with a "WTF" expression, which then becomes an "AAAAH, I get it". I thank you.
 
2392-10:

Q)- A single-phase circuit using 2.5mm[SUP]2 [/SUP] single-core PVC cables in conduit supplies adesign current of 20A .
If the cables are 15m long & have a rated voltage drop of ( 18mV/A/m ) the actual VoltageDrop will be . ????

A)- ( 18mV/A/m ) x 20A x 15m ) ÷ 1000 = 5.4V

2392-10: -&-s

Duringthe Testing Line of an Electrical Installation .Which Test would be carried out first . ????

612.2.1– Continuity of Protective Conductors . ◄
612.3.– Insulation Résistance . ( IR )
612.6. – Polarity .
612.9.– Earth Fault Loop Impedance .


 
Megger ( 1552 / 1553 ) :speechless:

SetUp :

RCD Touch Voltage selection ( To select either 25V or 50V )

1 )With the instrument turned OFF . hold down the Yellow test button & turn the left hand rotary switch to any ON position .
2 )Keep the button held down until the instrument displays the “ SET “ Warning .
3) Now release the TEST button .
4) Pressthe TEST button again to view the currentsetting for the Touch voltage .
Thedisplay shows the touch voltage limit . 50V

Note: The MFT can also display the measuredTouch Voltage on a bar-graph display .

Ifthe touch voltage display is Active . a bar-graph display will also appear .

5) Press the ORANGE( buzzer ) button to change the touchvoltage limit setting . 25V / 50V
6) Press the BLUE (RCD ) button to turn the bar-graphdisplay ON or OFF .
7) Press the TESTbutton to exit from the set-up menu .
 
Isolation& Switching : :49:

537.2.1. Every circuit shall be Isolated from the Live Supply.

Threepoints of Isolation .
Origin– 537.1.4.
DistributionBoards – 537.2.1.1.
FinalCircuits – 537.2.1.1.

MustIsolate all ( Phases) but not necessarily the Neutral– No link in CPC
Note (- 537.2.1.7.
Isolationat the Origin .

TN-S Phases or Lines & Neutrals
TN-C-S Phases only but both Lines & Neutral where access is Obtained by UnskilledPersons – 537.1.4.
TT- Both Line & Neutral .


 