Definitions– Part 2 . BS-7671:2008 :17:
Bonding Conductor . p/20 .
Aprotective conductor providing equipotentialbonding .
Class1 Equipment . p/21 .
Whereprotection against electric sock does not rely solely on basic insulation alone. Exposed – conductive parts being connected to a protective conductor whiththe fixed wiring of the installation . (See BS-EN 61140 )
Class11 Equipment . p/21 .
Whereprotection against electric shock relies on the application of additional orsupplementary insulation .
Thereis no provision for the connection of a protective conductorto exposed metalwork .
DoubleInsulation . p/23 .
DoubleInsulation ( Class 11 ) Insulation comprising both basic Insulation &supplementary insulation .
Earth. p/23
Theconductive mass of Earth . whose electricpotential at any point is conventionally taken as Zero. ◄◄
EarthElectrode . p/23
Conductivepart . which may be embedded in the soil or in a specific conductive medium .e.g. concrete or coke . in electrical contact with the Earth .
Aconductor or group of conductors in intimate contact with . & providing anelectrical connection to Earth .
EarthElectrode Résistance . p/23 .
Therésistance of an Earth electrode to Earth .
EarthFault Current .
Anovercurrent resulting from a Fault of negligible impedance between a Lineconductor & an Exposed – conductive – part or a protective conductor .
AFault current which flows to Earth .
EarthFault Loop Impedance . p/23
The impedance of the EarthFault current loop starting & ending at the point of Earth Fault . This impedance isdenoted by the symbol ( Zs )
Symbol( Z ) - Unit ( Ω )
TheEarth Fault Loop .
The impedance of the EarthFault current loop starting & ending at the point of Earth Fault . Consists of :-
• The circuit protective conductor ( C.P.C. )
• Consumers Earthing terminal & Earthingconductor
• for TN – Systems . Themetallic return path .
• for TT – Systems & IT Systems Earth return path .
• The path through the Earthed neutral point ofthe Transformer .
• The Transformer winding & phase conductor to point of Fault .
543-Protective Conductors .
543– provides information on the Selection of “ BOTH “ type & Cross – sectional Area of Protective Conductors .
Protective Conductors . areconductors provided for the purposes of Safety . protectionagainst Electric Shock .
GenericTerm “ ProtectiveConductors “ :thinking2:
2392-10. as designer(s) . Am making you Aware of the Facts .
Cross-sectional Areas of Protective Conductors .
Thereare two Methods that may be Employed when choosing a Protective Conductor asrequired by Regulation 543.1.1.
TheCross- sectional Areas ( C.S.A. ) of every ProtectiveConductor . other than Protective BondingConductors .
MustBe :-
► Selected . in accordance with Regulation 543.1.4. - :icon4:
Or
► Calculated . in accordance with Regulation 543.1.3. - :icon4:
2392-10: Yes we still use it in Industry :icon4:
543.2.7. Earthing Tail Requirement .
WhereMetallic Conduit . Trunking . etc is used for a ProtectiveConductor . The Earthing Terminal ofeach Accessory is required to be connected by a Separate Protective Conductor to the Earthing Terminal incorporated in theassociated box ( Back – Boxes) or other Enclosure .
Applicationsof Earthing : :vanish:
All Metallicenclosures & Extraneous conduciveparts . are at Equipotential .
Functionsof Earthing :
EquipmentEarth : Path for Fault Current . lowertouch voltage . protection against Electric Shock .
LightingEarth : Low résistance path to diversethe current . Under lighting attack .
TelecommEarth : Signal Earth . reduce noise & interference . stabilize D.C. supply voltage & prevent ElectricShock .
ComputersEarth : Reduce interference . maintain supply voltages .
Typeof Earthing :- :vanish:
SupplySystem – Neutral / Earth .
SystemEarth
ElectricalSafety Earth .
LightingEarth .
GeneratorEarth .
ProtectiveEarth . - Surge arrestor .
Telecom/ Computer Earth .
ShieldingEarth .
IntegratedEarthing System -
ElectrostaticEarth – Clean / room – Hospital .
Factors affect to the EarthImpedance . TT Systems :oops:
Soil.
Weather.
Electrodetype .
Electrodesize .
Near by Utilities .
Electrode in Parallel . -&-s
Distance between Electrode .
:thinking2:TT Systems
EarthRésistance of an Electrode
Soil Exhibits a resistance to the flow an Electrical Current .
Not an “ Ideal “ conductor
Résistance – can never be Zero . betweenthe Earth Electrode & “ True Earth “
The résistance between the Earth Electrode & “ True Earth “
SoilResistivity in ( Ωm )
Buriedlength of the Electrode in ( m )
Diameter of the Electrode in ( m )
Fault :icon4:
A circuitcondition in which current flows through an abnormal or unintended path .
Thismay result from an Insulation failure or a bridging of Insulation .
Conventionallythe Impedance between Live conductors or between Live conductors & Exposed or Extraneous conductiveparts at the Fault position isconsidered Negligible.
Regulation. Appendix 4 – ( 4D1A ) p/274 :17:
Caremust be taken tie sure that any Conductors’ which is operating above ( 70°C) is terminated into Equipment that canwithstand the higher temperature .
TheBritish Standard only requires that our Equipment is suitable for ( 70°C)
Ambient Temperature mustalways be taken into account .
TheCurrent Carrying Capacities given in the Tables in appendix 4 Calculated for a Cable operating in an Ambient Temperature of ( 30°C ) .
( 4D1A ) for4.0mm[SUP]2[/SUP] – Copper Conductor clipped direct can carry a currentof ( 37A ) at ( 30°C ) Pass a current of ( 37A ) through the conductor it would rise to ( 70°C )
Ambient Temperature were to increase to . ( 40°C ) then theTemperature of the conductor when we passed ( 37A ) through it would rise to ( 80°C )
Side– Effect . of this would be an Increase in Voltage Drop .
• The Maximumpermissible operating temperature of Cables are dependent mainly on the Type ofInsulation Material used in the Cable Construction
( 4D1A )
Ambient Temperature ( 30°C ) ◄◄
ConductorOperating Temperature ( 70°C )
Temperature is the Factor which dictates the size of theConductor in relation to the Number of Circuits Installed.
Thermoplastic : ( 70°C ) :44:
Measurement of ExternalEarth Fault Loop Impedance ( Ze ) iscarried out between the Incoming Line & Protective Earth . :19:
Earthing Conductor Detachedfrom the ( MET ) & test probe clipped toit .
Measurementof the External Earth Fault Loop Impedance ( Ze ) at the Origin of theInstallation for compliance with regulation 612.9
EarthFault Loop Impedance :
Live Tests & great careshould be taken when carrying them out .
Thereare Two Measurements for Earth Loop Impedance .
i) One is for External Loop Impedance ( Ze )
ii) Other is for the Circuit Loop Impedance ( Zs )
Bothof these tests are carried out Using an Earth Fault Loop Impedance TestInstrument with Leads & Probes compliant to ( GS-38 )
(Ze ) Earth Fault Loop Impedance :
TheInstallation must be ( Isolated ) – “ Live Test “ ◄◄ -&-s & the Earthing conductor disconnected .
Connectone Lead to the disconnected Earthing conductor& then insert a Probe into the Terminal ofthe Incoming Line .
TheMeasured Value will be ( Ze )
I use the Megger 1552 : Two Leads .
►► Instrument has ThreeLeads then the Third Lead must be connected to the Incoming Neutral ofthe Supply .
Thisis what -&-s want to Hear . ▼
TheEarthing Conductor must be Reconnected beforere-energising the Supply to the Installation .
(Zs ) Circuit Earth Fault Loop Impedance : :19:
Thisis a Live Test . ◄◄ for-&-s 2392-10 - ( At Socket Outlets)
“ Simple“ What is required . The Instrument is plugged into the Socketusing the Lead supplied & the resultRecorded .
TheHow’s & Why’s ??
Wherethe Circuit has NO socket outlets the instrumenthas to be ( Connected ) to the Exposed Terminalsof the Accessories on the Circuit being Tested .
ALL – POINTS must be tested & the Highest testresult Recorded as ( Zs ) for the Circuit
“ Certification& Reporting “
Onyour Test result sheet & add the Measured ( Ze ) to the Recorded ( R1 + R2 ) value . Then compare the totalvalue with the Measured ( Zs ) if it is Equal toor Lower then all is Fine .
Ifit is Higher then it may be that there is a Loose Connection & further Investigation is required .
Froma Testers point of View (- The Measured value will often be Less than theCalculated value due to the Presence of Parallel Path.
Measured( Zs ) must be compared to the Maximum value of ( Zs )
From-&-s point of View (- Ensurethat it complies with the Requirements for the circuit disconnection time .
O.S.G.p/13 .
BasicInformation Required . 313.1. Beforestarting Work on an Installation . Etc
ForExisting Installations Electricians’ should Satisfy themselves as to the Suitability ofthe Supply including the Earthing Arrangement. :speechless:
Regulations: Table 41.3 - Maximum Earth Fault LoopImpedance ( Zs )
Table 41.3 -For Circuit Breakers with ( Uo ) of 230V . ForInstantaneous operating giving Compliance with the ( 0.4s )disconnection time of Regulation 411.3.2.2.
BS-EN 60898 . / BS-EN 61009-1
MaximumMeasured Earth Fault Loop Impedance ( Ωs ) Overcurrent Protective Device is a Circuit Breaker .
Table 41.1.
MaximumDisconnection Times ( 0.4s ) - 411.3.2.2.
TheMaximum Disconnection Time stated in Table 41.1. shall be applied to FinalCircuit NOT Exceeding ( 32A ) - The regulations are using the Words . Final Circuit(s)
Apprentices. if we look at Table 41.1. - Maximum Disconnection Time stated in Table 41.1.is for a ( TN- system ) A.C. ≈ ( 0.4s )
MaximumEarth Fault Loop Impedance .
TheMaximum Earth Fault Loop Impedance is used to Calculate the available EarthFault Current within an Installation connected at ( Low – Voltage – below 1000V) :17: