“ Certification& Reporting “
resents3:
Listfour characteristics of the Electrical Supply that should be recorded on theDocument - this could come Up on-&-s .
313 – Supplies .
313.1. General The followingcharacteristics of the supply or supplies . from whatever source . & thenormal range of those characteristics where appropriate . shall be determinedby Calculation . Measurement . Enquiry or Inspection .
i) The nominal voltage(s) & its characteristics includingharmonic distortion .
ii) The nature of the current & frequency .
iii) The prospective short-circuit current at the Origin of the installation. ◄
iv) The Earth Fault Loop Impedance of that part of the systemexternal to the installation ( Ze )
v) The suitability for the requirements of the installation .including the Maximum Demand .
vi) The type & rating of the overcurrent protective device(s)acting at the Origin of the installation . ◄
These characteristics shall be ascertained for an External Supply& shall be determined for a private source . These requirements are equallyapplicable to main supplies & to safety services & standby supplies . ◄
NOTE : The above information should be provided by distributors’on request ( see Appendix 2 sec 2 )
Appendix 2 – Informative ) Some things have been Changed . inWording .
Definitions’ - p/39 . ( Ze )
That part of the Earth Fault Loop Impedance which is External tothe Installation ( Ω ) 313.1.
resents3:Listfour characteristics of the Electrical Supply that should be recorded on theDocument - this could come Up on-&-s .
313 – Supplies .
313.1. General The followingcharacteristics of the supply or supplies . from whatever source . & thenormal range of those characteristics where appropriate . shall be determinedby Calculation . Measurement . Enquiry or Inspection .
i) The nominal voltage(s) & its characteristics includingharmonic distortion .
ii) The nature of the current & frequency .
iii) The prospective short-circuit current at the Origin of the installation. ◄
iv) The Earth Fault Loop Impedance of that part of the systemexternal to the installation ( Ze )
v) The suitability for the requirements of the installation .including the Maximum Demand .
vi) The type & rating of the overcurrent protective device(s)acting at the Origin of the installation . ◄
These characteristics shall be ascertained for an External Supply& shall be determined for a private source . These requirements are equallyapplicable to main supplies & to safety services & standby supplies . ◄
NOTE : The above information should be provided by distributors’on request ( see Appendix 2 sec 2 )
Appendix 2 – Informative ) Some things have been Changed . inWording .
Definitions’ - p/39 . ( Ze )
That part of the Earth Fault Loop Impedance which is External tothe Installation ( Ω ) 313.1.