Inspector - has responsibilityplaced upon him as to the Safety of the Installation .
Visual Inspection )- is Essential to assess the safety of anInstallation before testing takes place .

Verification . All measures by means of which compliance of the electricalinstallation with the relevant requirements of BS-7671 are checked .comprising Inspection . Testing & Certification .
 
Justa Reminder . 2392-10

612.2.2. Continuityof the Ring Final Conductors’ . :19:

A “ Test “ shall be made to “ Verify “ the Continuity of Each Conductor includingthe Protective Conductor . of every Ring Final Circuit .

 
Justa Reminder . 2392-10

RingFinal Circuit )- Correctly connected . Ring Final Circuit showing ( Equal Current on Each Leg of the “ Ring “ ) :19:

 
Justa Reminder . 2392-10

( IR ) Insulation Résistance Testingrequires different test voltages for “Certain Circuits “ indentify what circuit(s) require the following voltages . 250V. 500V . 1000V

Isall in the Wording . -&-s



 
Competent. Persons responsible for Inspection & Testing . :19:

Competent person . A person who possesses sufficient technicalknowledge . relevant practical skills & experience for the nature of the electricalwork undertaken & is able at all times to prevent danger & where appropriate. injury to him / herself

Inspection& Testing . of the installation will be your responsible for decidingwhether or not an Installation complies with the Regulations in their Entirety. BS-7671:2008

2392-10:
Regulation. 134.1.1. Therefore the person carryingout the Installation . ( p/19 ) – ( p/21 ) Goodworkmanship by Competent persons or Person . Etc

Regulation . 610.5. Inspection & Testing of any Electrical Installation Work mustcomply . ( 156)
Regulation . 610.5. The Verification shall be made by a CompetentPerson . First Amendedment . ▼▼▼

Competent person . A person who possesses sufficient technicalknowledge . relevant practical skills & experience for the nature of the electricalwork undertaken & is able at all times to prevent danger & where appropriate. injury to him / herself

 
ConditionReport Inspection Schedule for Domestic & Similar Premises with up to 100ASupply .

Final Circuit(s)

Identification of conductors ( 514.3.1. )
Cables correctly supported throughout their run ( 522.8.5. )
Condition of insulation of live pars ( 416.1. )
Non-sheathed cables protected by enclosure in conduit . ducting ortrunking ( 521.10.1. )
□ To include the integrity of conduit & trunking systems ( metallic & Plastic )

Adequacy of cables for current-carrying-capacity with regard forthe type & nature of installation ( Section 523 )
Coordination between conductors & overload protectivedevices ( 433.1. : 533.2.1. )
Adequacy of protective devices . type & rated current forfault protection ( 411.3. )
Presence & adequacy of circuit protective conductors ( 411.3.1.1. : 543.1. )
Wiring system(s) appropriate for the type & nature of theinstallation & external influences (Section 522. )
Concealed cables installed in prescribed zones ( see Section D . Extent & Limitations’ ) (522.6.101. )
Concealed cables incorporating earthed armour or sheath . or runwithin earthed wiring system . or otherwise protected against mechanical damagefrom nails . screws & the like . see Section D . Extent & limitations .( 522.6..101 : 522.6.103. )
Provision of additional protection by RCD not exceeding 30mA .
□ for all sockets-outlets of rating 20A orless provided for use by ordinary persons unless an exception is permitted ( 411.3.3. )
□ For supply to mobile equipment not exceeding 32A rating for use outdoors (411.3.3. )
□ For cables concealed in walls or partitions ( 522.6.102 : 522.6.103. :
Provision of fire barriers . sealing arrangements & protectionagainst thermal effects ( Section 527 )
Band ii cables segregated / separated from band 1 cables ( 528.1. )
Cables segregated / separated from communications cabling ( 528.2. )
Termination of cables at enclosures - indicate extent of samplingin Section D of the report ( Section 526. )
□ Connections soundly made & under no undue strain 526.6.
□ No basic insulation of a conductor visible outside enclose ( 526.98 )
□ Connections of live conductors adequately enclosed 526.5
□ Adequately connected at point of entry to enclosure ( glands .bushes etc. ) 522.8.5.
Condition of accessories including socket-outlets . switches &joint boxes ( 621.2 – ( iii )
Suitability of accessories for external influences ( 512.2. )






 
Examples of items requiring Inspection for an ElectricalInstallation Condition Report .

A Visual Inspection shouldfirstly be made of the External Condition of al Electrical Equipment which isNot – Concealed . :19:

Further detailed Inspection . including partial dismantling ofequipment as required . should be carried out as agreed with the personordering the work . ( 612.2. )



 
State:- Indentify the type of circuit thatwould require the following applied voltages when conducting an Insulation Résistancetest . :19:

i) 250V .
ii) 500V .
iii) 1000V .

i) SELV / PELV .
ii) Systems up to & including 500V .
iii) Systems over 500V but under 1000V .

Short& Simple . -&-s

Locations ) containing a Bathor Shower .

Additional protection for all low voltage ( LV ) circuits by RCD not exceeding 30mA ( 701.411.3.3. )
Where used as a protective measure . requirements for SELV orPELV met . ( 701.4.4.4.5. )
Shaver sockets comply with BS-EN 61558-2-5 . formally BS 3535( 701.512.3. )
Presence of supplementary bonding conductors . unless not requiredby BS-7671:2008 . ( 701.415.2. )
Low voltage ( e.g. 230 volt ) socket-outlets sited at least 3m from zone 1 ( 701.512.3. )
Suitability of equipment for external influences for installedlocation in terms of ( IP ) rating (701.512.2. )
Suitability of equipment for installation in a particular zone . (701.512.3. )
Suitability of current-using equipment for particular positionwithin the location ( 701.55. )

 
AFundamental principle of ELECTRICAL SAFETY is that NO SINGLE FAULT CONDITION should cause ahazardous situation . Plain English .

Asthe FirstAmendment says .

Definitions . Fault Protection . p/28 .
Protection against electric shock under ( Single Fault Conditions)

Note )- for low voltageinstallations . systems & equipment . fault protection generallycorresponds to protection against indirect contact . mainly with regards tofailure of basic insulation . Indirect contact is “ contact of persons orlivestock with exposed-conductive-parts which have become live ( UNDERFAULT CONDITIONS “


 
Electrically Independent Earth Electrodes . p/27

Earth electrodes located at such a distance from one another thatthe maximum current likely to flow through one of them does not significantlyaffect the potential of the OTHER(S) .
 
E.I.C.R.

Current – Using Equipment (Permanently Connected )

• Condition of equipment in terms of ( IP ) rating etc . ( 416.2.)
• Equipment does not constitute a fire hazard ( Section 421 )
• Enclosures not damaged / deteriorated so as to impair safety (621.2. (iii))
• Suitability for the environment & external influences (512.2. )
• Security of fixing (134.1.1. )
• Cable entry holes in ceiling above luminaires . sized or sealedso as to restrict the spread of fire .List number & location of luminairesinspected ( Separate page )
• Recessed luminaires ( Down lights )

1) Correct type of lamps fitted .
2) Installed to minimise build-up of heat by use of “ fire rated “fittings . insulation displacement box or similar ( 421.1.1.1. )
3) No signs of overheatingto surrounding building fabric (559.5.1. )
4) No signs of overheatingto conductors / terminations ( 526.1. )
 
TheImpedance of the Earth connection must be low enough to ensure that sufficient currentcan flow through the protective device so that it disconnects the supply quickly( 0.4 sec ) & Voltage on the Earthconnection does not RISE more than( 50V )

RCDsoperate at much lower Fault Currents . ◄◄◄ :19:



 
701.411.3.3. Additionalprotection by RCDs

Additional protection shall be provided for all circuits of thelocation . by the use of one or more RCDs having the characteristics specified inregulation 415.1.1.
Note : see also Regulation 314.1. ( iv ) & 531.2.4. concerningth avoidance of unwanted tripping . p/166

701.411.3.3. Additionalprotection by RCDs

Additional protection shall be provided for all [ low voltagecircuits of the location ] . by the useof one or more RCDs having the characteristics specified in regulation 415.1.1.
Note : see also Regulation 314.1. ( iv ) & 531.2.4. concerningthe avoidance of unwanted tripping . p/199




 
Section705 : Additional protection : Supplementaryequipotential bonding .

Theonly wording that is changed . 705.415.2.1. ( p/183 ) – ( p/216 )

Note : Where a metal grid isnot laid in the floor a TN-C-S supply is not recommended .

Note : Where a metal gridis not laid in the floor . the use of a PME Earthing facility as the means of Earthing for the electrical installationis not recommended .



 
Thedifference between the First Amendment & 17[SUP]th[/SUP]Edition

Section 705 : 705.1. Scope :

Theonly wording that is changed .

Rooms . locations & areas for household applications &similar are not covered by this section . p/183 .
Note : Section 705 does not cover electric fence installations .Refer to BS-EN 60335-2-76 & BS-EN 6100-1.

Rooms . locations & areas for household applications &similar are not covered by this section . p/216 .
Note : Section 705 does not cover electric fence installations .Refer to BS-EN 60335-2-76



 