A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
RCD - protection . Therequirements of Regulation 314.1. Division of Installation . need to be taken into account . whendesigning & installing the circuitprotective arrangements . 314.1. States thatevery installation shall be divided into circuits as necessary to .
i) avoid danger & minimize inconvenience in the event of afault .
ii)
iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit .
iv) Reduce the possibility of unwanted tripping of RCDs due toexcessive protective conductor ( PE ) currents not due to a Fault .
( protective conductor currents ( PE ) produced by equipment innormal operation )
Meansa Single RCD cannot be Used to protect the whole installation . ( As in theevent of a fault . The Supply will be lost to all circuits ( Inconvenience / Danger )
RCDs are NOT designed to break the HighShort Circuit Currents . Etc . Must beused with an Overcurrent Device / MCB
RCBO / will . Overload - Short circuit . p/34
Whereprotection is provided by an RCD . The effective operation of each RCD . shall be verified by a Test simulating anAppropriate fault condition independentof any Test facility incorporated in the device .
30mA– 0.03A .
10mA– 0.01A .
2392-10 (- On.Site.Guide :- does “NOT “ express any preference between Ring FinalCircuit or Radial Circuit(s) . Both circuit(s) are available to Designers / Electricians
Radial& Ring Final Circuit(s) & NO preferenceis assigned to any Circuit(s) Designers / Electricians are free to choose any of the Three StandardsCircuit(s) A1 – A2 – A3 .
Regulation 314.3.
Thisallows the designer to develop final circuit(s) coving different ( Floor areas ) & using different ratingsof protective devices
Useful Junk . “ ConductorSize “
Theconductor size for a fused spur is determined from the total current demand served by that spur .Which is limited to a maximum of 13A .
Justa Thought .
TheLoad current in both legs of the Ring Final Circuit is shared as Equally as Possible. :icon_bs:
2392-10(- if we look around the Kitchen . Everything is grouped aroundthe Sink . W/machine . T/dryer /D/Washer . Etc .
Ifthe Sink does NOT happen to be more or less in thecentre of the Ring Final Circuit . One leg will carry MOREcurrent than the OTHER . ???
SELV.
A voltage NOT exceeding 50V a.c. or 120V d.c. between conductors at any point of a circuitwhich is separated from circuits with higher voltages & from earth byinsulation at least equivalent to that for ( Class II ) or which has equivalent protective means .
SELV. p/34
( separated extra-low voltage ) An extra-low voltage system which iselectrically separated from earth 7 from other systems in such a way that asingle fault cannot give rise to the risk of electric shock .
Final Circuit . p/28
A circuit connected directly to current-using equipment . or to asocket-outlets or other outlet points for the connection of such equipment .
Fixed Equipment . p/28
Equipment designed to be fastened to a support or otherwisesecured in a specific location .
SupplyPoint .
A pointat which electrical energy is delivered .
Origin of a Installation / Circuit .p/31 .
The position at which electrical energy is delivered to an electricalinstallation .
Stationary Equipment . p/35 . -&-s
Electrical equipment which is either fixed or which has a massexceeding ( 18kg ) & is not providedwith a carrying handle .
( This value of thisMASS is GREATER than 18kg . in standards relating to Household Appliances ) Domestic. CoP /2392-10
RadialFinal Circuit .
A finalcircuit that serves two or more points including socket-outlets .
Ring Final Circuit . p/34 .
A Final Circuit arranged in the form of a ring & connected toa single point of supply .
Spur . p/34
A branch from a ring or radial final circuit .
Portable Equipment . ( see Mobile Equipment ) p/32 .
“ Mobile Equipment “ Portable Equipment – deprecated )) p/31 .
Electrical equipment which is moved while in operation or whichcan easily be moved from one place to another while connected to the supply .
UsefulJunk
Reason . BS-1363. p/278 BS-1363
1gang & 2 gang 13A . switched socket –outlet .
The switch avoidsUnnecessary Wear on the socket as it can beswitched OFF rather than Unplugged .
13ARectangular Pin Plug . 1362 : 1973 – ( 1992 ) p/278
Commonlyreferred to as . “ Flat / pin . Square / pin . Fused Plug . Commonly used sizes . 3A . 5A . 13A . CoP .
BS-1363. Fused connection unit with double pole switch & front flex outlet ‘
Reason . Used to supply permanentlyconnected appliances & also provides a meansof control . By removing the Fuse we have Isolation . Lock / OFF . M/K
FusedConnection Unit . Unswitched with Neon . should be used it is requiredthat the appliance should NOT be accidentally SwitchedOFF . Alarm/circuits & Freezers’ .
Socketoutlets provide an easy & convenient method by which portable appliancesmay be connected to the electrical supply . BS-1363
TheBritish . Ring Final Circuit system . & BS-1363 .
13Aplugs . socket-outlet(s) . connection unit(s) & adaptors plug &socket-outlet system were Introduced into the UK. In 1947 .
PDF] THE ORIGIN OFTHE BS 1363 PLUG AND SOCKET OUTLET ... Useful Junk . Good Reading.
2392-10 (- It is recommendedthat twin socket-outlet(s) be installed rather than single types as the initialcost is low in relation to having them replaced at a later date . .
2392-10 (- The following Guidelines as to recommended numberof Socket-Outlet(s) per location in a Typical Domestic Dwelling . O.S.G. P/178 . Table H7
Note : Other methods are Not precluded .
2392-10(- Ring Final Circuit .
Thecable used must be capable of carrying (0.67 times ) the rated current of the protective Device . On the circuit .
Example. This is ( 2.5mm[SUP]2[/SUP]) Which has a current carrying capacityof ( 32A) When installed in Normal Domestic Installations.
Usingthe Factor of ( 0.67times ) we can calculate the maximumload on the circuit .
Calculation. Maximum Load on Cables .. 23 ÷ 0.67 = 34.33 Amps .
Alternatively.
Givena protective device current rating . find the minimum . Current Carrying Capacity of the cable required .
Calculation. Minimum . C.C.C. of Cable . 32 x 0.67= 21.44Amps
MCBwith a rating of ( 32A ) is fitted to a Ring Final Circuit(s) in DomesticInstallation(s) This provides protectionfor ( 2.5mm[SUP]2[/SUP] ) cables
Ring Final Circuit arrangements Regulation . 433.1.103 .
(iv) taking account of the totalfloor area being served . ( Historically . a limit of 100m[SUP]2[/SUP] has been adopted ) p/425 :13:
Example. This is ( 2.5mm[SUP]2[/SUP]) Which has a current carrying capacityof ( 23A) When installed in Normal Domestic Installations.
Mistakein calculations . ( 23A ) ◄◄
Cooker Example .Calculation .
Note :Other methods are Not precluded . :banghead:
To ascertain the total loading of an electric cooker,the loading of the individual elements, motors, lights etc. must be added. Forexample, the total load of a typical electric cooker is comprised of thefollowing loads:
Boiling Ring RH Rear . 2000 W
Boiling Ring RH Front . 2000 W
Boiling Ring LH Rear . 2000 W
Boiling Ring LH Front . 2000 W
Grill Element . 1800W
Oven Element LH . 1200 W
Oven Element RH . 1200 W
Hot Cupboard Element . 500 W
Oven Lamp . 40 W
Total Load 12,740 W
The full-load current of this cooker may now becalculated:
FullLoad Current = Load in Watts
…………………………Full Load Current
I = 12740
…. 230
I = 55Amps approximately
However,diversity is allowed and should be assessed as follows:
The first 10 Amps of thetotal rated current of the cooker, plus 30% of the remainder of the total ratedcurrent.
First 10A = 10 A
30% 0f Remainder = (55 – 10 ) x 30% = 13.5 A
Total = 10 +13.5 = 23.5 A
Wiring Regulation Restrictions.
Domestic Installation(s) . The total ( REN ) –Ring equivalent number . value of all Telephone equipment connected on a Line must NotExceed ( 4 )
2392-10: MK . Switch Disconnectors 100A . BS-EN 60947-3.
17[SUP]th[/SUP] Edition 2011 . Regulations . 537.2.2.1. & 537.2.2.2. p/151.
Devices for Isolation . 537.2.2.1.
A device for ( Isolation ) shall ( Isolate ) all live supply conductor(s) from the circuit concerned .subject to the provisions of Regulation 537.1.2.
A device suitable for isolation shall be selected according to the requirements which are basedon the overvoltage category applicable at the point of Installation . Etc .
Equipment used for ( Isolation ) shall comply with Regulation(s) 537.2.2.1. & 537.2.2.2. to ( 6 ) ◄◄ :13:
537.2.2.2. The position ofthe contacts or other means of ( Isolation ) shall be either externally visible or clearly& reliably indicated . An indication of the isolated position shall occuronly when the specified ( Isolation ) has been obtained ( in EACH POLE )
2392-10: MK . Miniature Circuit Breaker(s) MCBs . BS-EN 60898 : 2003 .
When the Green Indicator is Visible . ( Then a contact gap of 4mm has been ACHIEVED ) “ Supply is Cut-OFF “
BS-EN 60898 : requires the tripping to occur within ( 100milliseconds ) Fault Current of up to6000A .
***Cont../ Useful Information for Electricians & Apprentices***
Australia
amberleaf,
Dan,