MK. Residual Current Devices ( RCDs ) D/P
BS-EN 61008: 1995 .
17[SUP]th[/SUP] Edition 2011 . Regulations . 537.2.2.2. & 537.3.2.2.
537.3.2.2. A device for switching OFF for mechanical Maintenance or acontrol switch for such a device shall require ( Manual Operation )
The ( Open Position ) ofthe contacts of the ( Device ) shall be ( Visible ) or be ( Clearly ) & ( Reliably Indicated )
Note : Theindication required by this regulation may be ( Achieved ) by the use of the (Symbols . “ O “ & “ I “ ) to indicate the ( Open ) & (Closed position respectively )