Understanding of the Underpinning Knowledge . BS-7671:2011 .

Selection& Sizing of C.P.C.& Earthing Conductors .

C.P.C.& Earthing conductors are selected in accordance with Section – 543 .
543.1. deals with Sizing : 543.2. with types & 543.3. with preservation of Continuity .

A ProtectiveConductor may be common to more than OneCircuit . Regulation – 543.1.2. p/160 .

Thefollowing can be used as a Protective Conductor . Regulation – 543.2.1. . p/ 163 .

i)Single core cable .
ii) Conductor in a cable .
iii)Insulated or bare conductor in a “ Common Enclosure with Insulated live conductors .
iv) Fixed bare or Insulated conductor .
v) Metal covering . Sheath screen or armouringof a cable .
vi)Metal conduit . Metal cable management . or other Enclosures or Electricallycontinuous support system for conductors .

vii) Extraneous –conductive – part complying withRegulation . 543.2.6. p/163.




 
Whensizing the C.P.C. & Earthing conductor the following must be conceded .

i)Earth Fault Loop Impedance requirements : Section - 411
ii) Thermal Constraints – conductor does notoverheat during Fault Conditions . Regulations – 543.1.3. & 543.1.4. p/160 / p/162 .
iii) Additional requirements for ( PME ) supplies . Regulation – 544.1.1.
iv) Additional requirements for Protective conductors where in the ground .Regulations – 542.3.1. & 543.1.1. p/159 . p/160

EarthFault Loop Impedance : P/39 . Zs = Ze + R[SUP]1[/SUP] + R[SUP]2[/SUP] . -&-s . where to find it .
 
Understanding of the underpinning knowledge .

Earthing& Bonding . Requirement for SpecialInstallations or Locations .

Section701 . Location Containing a Bathor Shower .
SupplementaryBonding – is not required in NEW installation as an RCD is always required for bothDomestic & Commercial Installations .

(Additional Protection : Supplementary Equipotential bonding )

Section702 . Swimming Pools & Fountains
Regulation. 702.415.2. p/205 . require local Supplementary bonding betweenall Extraneous – conductive –parts . in Zone 0. 1. & 2. the CPCs of allExposed – conductive-parts in these Zones . ( See – Regulation – 415.2. )

(Additional Protection : Supplementary Equipotential bonding )

Section705 . Agricultural & Horticultural Premises .
For( These premises ) where ( Livestock ) iskept . the requirements . 705.415.2.1. – p/216. should be Noted .
Supplementarybonding shall . connect together all Exposed-conductive-parts . & Extraneous-conductive-partswhich can be touched by ( Livestock ) ifthere is a Metallic Grid laid in the floor it should be Supplementary bonded .

( Protection against Electric Shock ) )

Section706 . Conducting Locations with Restricted Movement .
Whereautomatic disconnection is used for protection against Electric Shock .Regulation . 706.410.3.5.- ( iii ) requires SupplementaryEquipotential Bonding

Section711 . Exhibitions’ . Shows & Stands. p/239
Structuralmetallic parts . which are ( Accessible ) fromwithin the Unit . shall be connected to the Main Earth Terminal “ Within “ theUnit .

( Earthing arrangements & ProtectiveConductors )
Section– 712 . Solar Photovoltaic ( PV ) power Supply Systems .
Whereprotective bonding conductors are installed . These shall be run parallel &in close contact with the . D.C. & A.C. cables . Regulation – 712.54 . p/243

(Protective Equipotential Bonding )
Section717 . Mobile ofTransportable Units .
717.411.3.1.3. p/247 . requires Main Protective Bonding to the ( Accessible ) conductive partssuch as the Chassis .

( Protective Earthing & ProtectiveEquipotential Bonding )
Section 721 . 721.411.3.1.p/254. calls for ( Additional ) bonding of . Extraneous – conductive– parts within the Caravan & MotorCaravan .

(Additional Protection : Supplementary Equipotential bonding )

Section740 . Temporary Electrical Installation for Structures . Amusement Device &Booths at Fairgrounds . Amusement Parks & Circuses .
Locationsintended for ( Livestock) require Supplementary Bonding - Regulation . 740.415.2.1. p/ 269 – see 705


 
(IR ) .
Whymay a ( largeinstallation ) give a pessimistically low overall Insulation Résistancevalue . Because there are a large numberof circuits all in parallel . 2391-10

Why. do capacitors . Neon’s . need to be disconnected . To avoid misleadingtest results .
Handle “ Capacitors “ with care . They could be fully charged.

What. Test voltage & minimum value of Insulation Résistance are appropriate forcircuits ( Incorporating ) Surge Protective Devices . ( 250V d.c.– 1MΩ ) 2011 .

Thefrequency in Hertz ( Hz ) is . Cyclesper second - of the Electrical Source .
 
MedicalLocations .

Forthe sake of -&-s . 2011 .

Typesof System Earthing . 710.312.2. p/230 .

PEN) conductors shall not be used in ( Medical Locations & Medical Buildings ) downstreamof the main distribution board .

Note : in Great Britain , Regulation 8(4) ofthe Electricity Safety . Quality & Continuity Regulations 2002 prohibitsthe use of ( PEN ) conductors in Consumer’sInstallation .
□ Plain English . “ Typesof System Earthing “
The ( TN-C . System ) is not allowed inMedical Locations & Medical Buildings downstream of the main distributionboard .

Example(- Load & Earth Fault Currents ) associatedwith TN-C systems . can circulate through the casing of a ( Class 1 ) equipment thus causing Electromagnetic Interference with SensitiveElectronic Medical Equipment .



 
MedicalLocations .

Forthe sake of -&-s . 2011 .

710.531.2. RCDs .

710.531.2.2. Socket-outletsprotected by RCDs

For each circuit protected by an RCD having the characteristicsspecified in Regulation 415.1.1. consideration shall be given to reduce thepossibility of ( Unwanted Tripping ) of the RCD due to excessive protectiveconductor currents produced by equipment in normal operation .

Regulation 415.1.1. Additional protection : Residual Current Devices ( RCDs )
The use of RCDs with a rated residual operating current ( IΔn ) not exceeding 30mA & an operating time notexceeding 40mS at a residual current of ( 5 x IΔn ) is recognized in A.C. systems as additionalprotection in the event of failure of the provision for basic protection &/ or the provision for Fault protection or carelessness by ( User )

InMedical Locations of Group ( 1 ) & Group ( 2 ) ◄►-&-s . 2011 . Medical Locations isin the Regulations . Q/As

710.411.4.– TN- system. -&-s .
InFinal circuits of ( Group 1 ) rated up to ( 63A) . RCD having the characteristics specified in Regulation . 415.1.1. shall be Used.




 

MedicalLocations .

Forthe sake of -&-s . 2011 .

710.411.3.2. Automatic disconnection in Case of aFault .

710.411.3.2.1. (-&-s ) in Medical Locations of ( Group 1) & ( Group 2 ) WhereRCDs are required . ONLY type ( A ) or Type ( B ) shall be selected . depending on the possibleFault Current arising .

NOTE : Type ( AC ) RCDs SHALL NOT be USED . this is what -&-s are looking . Q/As .2011 .






 
MedicalLocations .

710.559 . Luminaries’ &Lighting Installations .

InMedical Locations of ( Group 1 ) & (Group 2 ) at least two different sources of supply shall be provided . One ofthe sources shall be connected to the electrical supply system for SafetyServices .

Note : Safety Services are synonymouswith ( Emergency Services ) Refer to “ SafetyLighting “ for the recommended percentage of Luminaries suppliedfrom Safety Source .

710.560.9.1. Safety Lighting .
Note : The Luminaires ofthe Escape Routes shall be arranged on Alternate Circuits .









 
Main EarthingTerminal .

Circuit protective conductors.
Protective bonding conductors.
FunctionalEarthing conductors – if required .
Lightingprotection system bonding conductor . if any – Regulation 411.3.1.2.

542.4.1. - Main Earthing Terminal must be easilyaccessed . This is primary to allow disconnection of any of the aboveconductors as required when Testing the Installation .

• MinorElectrical Installation Works Certificate does NOTrequire a record OF . p/393

i) System Earthingarrangements . P
ii) Departures fromBS-7671:2008. P
iii) Method of faultprotection . P
iv) Prospective fault current .

InitialVerification .

632.1Following the Initial Verification required by chapter 61 .
an Electrical Installation Certificate. ( EIC ) together with ( Schedules ofInspection ) & ( Schedules of Test Results ) shall be givento the person ordering the work

632.4.Defects or Omissions revealed during inspection £ testing of the installationwork covered by the Certificate shall be made good before the Certificate isissued .

• Any itemthat does NOT need Inspection during “ Initial Verification“ should be Marled . ( Schedule of Inspections ) p/395

i) P
ii) N/A .

2011 - p/395 . Bottom . N/A – toindicate an Inspection is NOT applicable to aparticular item
2011 - p/395 . Bottom . P – to indicate an Inspection has been carried OUT & the result is satisfactory .

► donot get mixed up with , OLD 17[SUP]th[/SUP] Edition ( Schedule of Inspections ) 2008 . “ of the Internet “

P . to indicate an Inspectionhas been carried out & the result is satisfactory .
N/A . to indicate an Inspection has been carried out& the result is NOT satisfactory ( applicable for a periodic inspectionOnly )
X . to indicate the inspection is notapplicable to a particular item .
LIM . to indicate that . exceptionally . alimitation agreed with the person ordering the work prevented the inspectionbeing carried out ( applicable for a periodic inspection only )
 
• NewInstallation is protected against fault by ( ADS )When Inspecting this method of protection . Which of the following is NOT a essential check .

i) Earthing conductor . P
ii) Circuit protective conductors . P
iii) Main protective bonding conductors . P
iv) Fire barriers .

Hint : 531.2.5.- The use of an RCD associated with a circuit normally ( Expected )to have a ProtectiveConductor . ←

GN-3 –p/22 . 441 . AutomaticDisconnection of Supply– ( ADS )
Thepresence . correct sizing . connectionof the appropriate protective conductors . MUST be CONFIRMED as FOLLOWS.

542.3. – Earthing conductors. P
543 – Circuit protectiveconductors . P
544 – Protective bondingconductors . P
544.1. – Mainbonding conductors . P

• this Non-statutory document that is applicable to theconstruction & use of ( Test Equipment ) IS .

i) HSE . Guidance Note-38 .
ii) IET . Guidance Notes 3 .
iii) IET . O.S.G. BS-7671:2008 ( 2011 )
iv) BS-7671:2008. No 1 :2011 .

• Test Method 1 (- as well as checking theContinuity of the protective conductor . also measures ( R[SUP]1[/SUP] + R[SUP]2[/SUP]) which when added to the External Impedance ( Ze ) enables the Earth FaultLoop Impedance ( Zs ) to be checked .

 
Megger1552

BondedMetalwork Testing [ HI ]

Testleads set . Option . 1 or 2 .

i) Connect the ( GreenLead ) to the Bonded Metalwork .
ii) Connect the ( RedLead ) to Line .
iii) Supply voltage is displayed .
iv) The test will “ Bleep “ & automaticallystart when voltage is detected .
v) Measured résistance value is displayed .

Thisis how . -&-s like to hear about GN-38 – Leads . !!!! 2391-10 . -&-s Exams :banghead:

• MFT . 1552 : ( Ze ) Testing .

Supplyis turned OFF. 100A - Disconnector is Isolated from Supply . ◄ ( MainIncomer )

Disconnectthe Main incoming Earth Conductor from the ( MET )

Then. Connect your ( Black ) GS-38. Lead fullyinsulated leads onto the Earth Conductor . making sure you get a good connection ) ► Wording . GN-38 – Leads :banghead:

Turnon Megger to the setting of ( Hi –Loop)

Thentake your ( Red ) GS-38. Lead fully insulated lead / with “ TIP “ placethis onto the Main incoming left hand terminal ( Main - Line Conductor )

Fewseconds the . Megger 1552 – will Automatically Read - ( .28Ω ) - Ohms’

Recordthis onto your . ( Certificate ) Thenconnect Earth Conductor. back UP . to the ( MET )

MFT . 1552 – 3 . : if circuitsare RCD protected then you’ll need to use “ Three-wires “ onthe ( No– Trip Setting ) for Zs .
( Ze ) & ( PFC ) is generally carried out at the ( Intake )where ( No RCD ) protection exists so that willbe ( Two-Leads ) ON the ( Hi ) currentsettings .

( Ze & Zs ) aremeasured in ( Ohms ) & (PFC ) ismeasured in ( kA)

• Non-trip – 3 – Leads for RCD side . ←

• Hi ) setting& 2 – Leadsfor Non-RCD ←

 
EarthFault Loop Impedance . D/B –1 : D/B – 2 : there areTwo distribution board on site ,

Ata distribution board ( D/B-2 ) . This measurementis called ( Ze ) is only really correct when its measured at the ( First Distribution Board )of the Installation . for the External Impedance of the Installation .

Whenconnected & button pressed it fires a current of up to ( 25A ) or so through the loop. it depends on theImpedance of the circuit . the time ofthe pulse is limited to ( 40mS ) Two cycles on a 50Hz supply . this is for . Safety Reasons.

DirectMeasurement ( Ze ) . The reason that (Ze ) is required to be Measured are Twofold .

i) Verify that there is an Earth Connection .
ii) Verify that the ( Ze ) value is equal to orless than the value determined by the designer & used in the DesignCalculations .




 
Faultfinding when RCCB Trips . ( blast from the past )

Switch OFF all the ( Switches / MCB ) connectedin the circuit downstream the . RCCB . Switch ON . RCCB & switch ON the switches . Oneby One . You will find that during switching ON of a particular Appliance / Switch . RCCB trip again & again

Whichshows that is the Faulty ( Circuit / Appliance ) .Isolate the Faulty Circuit . as you know. ( Rectify the Fault & Switch ON the RCCB )
 