Wording: 2391-10 : -&-s Exams .
Earth Fault Loop Impedance .
-&-s) Test that has to be carried on anEnergized Installation . ( Safety Precautions must be Taken )
➥ Purpose of thetest is to ensure that . in the event of a ( Line – to – Earth Fault ) enough current will flow around the ( Earth Fault LoopImpedance )
Tooperate the protection within a specified time . Example )- Ring Final Circuit – 411.3.2.2.– p/53 . The maximum disconnection timestated in ( 41.1.) shall be applied to Final Circuits NOT exceeding 32A . (Time – 0.4s )
Themeasured value of Loop Impedance is then compared with that given in )- ( 41.1. )
Wording : -&-s Exams . Earth Fault LoopPath .
TheEarth Fault Current Loop ( Line – to – Earth Loop ) comprises the followingparts .
( Starting ) at the point of Fault . → the circuit protective conductor . → the consumer’s earthing terminal &earthing conductor : For .
TN- systems the (Metallic return path ) Or .
TT– systems the earth return path – the path through the earthed neutral point ofthe transformer & the windings . & the Line conductor from thetransformer to the point of Fault . Theearth fault loop impedance ( Zs ) at apoint distant from the origin of the installation is measured with the ( Main protective bonding conductor )conductors in place .
Earth Fault Loop Impedance .
-&-s) Test that has to be carried on anEnergized Installation . ( Safety Precautions must be Taken )
➥ Purpose of thetest is to ensure that . in the event of a ( Line – to – Earth Fault ) enough current will flow around the ( Earth Fault LoopImpedance )
Tooperate the protection within a specified time . Example )- Ring Final Circuit – 411.3.2.2.– p/53 . The maximum disconnection timestated in ( 41.1.) shall be applied to Final Circuits NOT exceeding 32A . (Time – 0.4s )
Themeasured value of Loop Impedance is then compared with that given in )- ( 41.1. )
Wording : -&-s Exams . Earth Fault LoopPath .
TheEarth Fault Current Loop ( Line – to – Earth Loop ) comprises the followingparts .
( Starting ) at the point of Fault . → the circuit protective conductor . → the consumer’s earthing terminal &earthing conductor : For .
TN- systems the (Metallic return path ) Or .
TT– systems the earth return path – the path through the earthed neutral point ofthe transformer & the windings . & the Line conductor from thetransformer to the point of Fault . Theearth fault loop impedance ( Zs ) at apoint distant from the origin of the installation is measured with the ( Main protective bonding conductor )conductors in place .