Discuss Contactor wiring, break ring circuit through a stop button in the UK Electrical Forum area at ElectriciansForums.net
Hi guys , I have to break a ring circuit through a contactor with an emergency stop button .. just want to double check my wiring in the diagram is correct .. haven’t done much of this sort of work so any feedback is appreciated.
I would simplify things and place the socket RCBO in its own garage consumer unit, and the contactor on the supply to this CU.
What is the ring circuit used for? Power tools in a workshop?
Who has decided the Circuit needs an E.M stop and what is the reason for this decision?
Has whoever made the decision thought of the consequences of the EM stop being reset and whatever is plugged in suddenly starting up?
As it would be on 13amp sockets, anything in the future could be plugged in and subject to uncontrolled restart.
Normally anything under Em Stop control would have individual no volt release protection to stop the above happening.
Don't call it an Emergency Stop..... Just a Stop Button.
Next fit a Shunt Trip for the 32A RCBO.
It is a stop button that needs a key to disengage it again
It’s more that when it’s disengaged it turns on again anything plugged in e.g an angle grinder could unexpectedly start up. There is stuff in regs about avoiding rotating machines starting without warning.
A possible solution might be to also change the sockets to non-latching RCD sockets so restoration of power requires each socket to be individually reset.
I still don’t hugely like this though as by adding a facility to stop everything it’s introducing multiple scenarios of a button unexpectedly starting things.
Hi guys , I have to break a ring circuit through a contactor with an emergency stop button .. just want to double check my wiring in the diagram is correct .. haven’t done much of this sort of work so any feedback is appreciated.View attachment 108600
No, to the best of my knowledge that is non-compliant as the contactor will re-energize immediately when the stop button is reset.
There should be a minimum of a seperate reset button.
How far away from the RCBO is the contactor going to be? You'd be better off having a single 4mm conductor from the RCBO to the contactor.
If the contactor is far away from the OCPD then somebody could mistakenly add sockets to the ring before the contactor.
That would still need a seperate reset control.
Why ?
There's a big issue with the key reset type of E-stop in that human nature is to leave the key in it so that you don't loose it. This means the button can't be as easily operated as it should be.
If someone is silly enough to leave the key in after going to all the trouble of fitting a key to reset stop.
The same could be said for a tripped RCD or MCB do we need a separate reset for them as well ?
Because, to the best of my knowledge it is one of the minimum requirements for emergency stops of any type, this isngiverned by legislation and not bs7671. I'm far from an expert on the relevant legislation though so yes I may be wrong.
But you can't design a safety system based on whether it would be silly for someone to do something, these systems need to be designed failsafe and if one possible failure is a key being left in an e-stop then it should be designed out of the system.
The same cannot be said for those things, they are completely different and governed by completely different rules!
An MCB or RCD will automatically trip again if the fault still exists, an E-stop will not automatically press itself if reset in error.
If the E-stop fails to latch in the off position for any reason then having it electrically latched and requiring a second deliberate action to reset it will prevent a dangerous situation.
I should add, The scenario for this wiring is in a classroom situation , for the instructor to kill the power when leaving the room. There won’t be any power tools used in this scenario so there shouldn’t be any reason for issues with anything starting up when engaging the stop button again .
Having said this , will the wiring be ok ?
Emergency switching: 537.4​
Emergency switching should be provided for any part of an installation where it is necessary to isolate the supply quickly to remove unexpected danger.
In installations with rotating machinery, this is usually done by using ‘stop’ buttons. Care should be taken to ensure that the stop buttons are…
  • Near to the machine / equipment
  • Should not be capable of being reset remotely, unless with a key switch.
  • If remote resetting is possible, then the activated stop button must remain activated at the point of the danger until being reset once the danger is removed.
  • In areas where there are untrained people, the stop buttons should lock when operated.
There is a difference between an emergency stop, generally used on moving machinery, and emergency switching off to turn off a few sockets, which is what the OP is intending.
That's only if a fault is still present, it could be that the fault is intermittent, such as a partially cut cable.
Emergency stop is an emergency operation intended to stop a process, system, machine, or a movement that has become hazardous.
Emergency switch off triggers an operation of switching off the supply of electrical energy and aims to reduce risk of an electric shock or other hazard.
So it’s not an emergency stop?
Just an isolator?
Simple on/off switch to control the contactor would be fine.
The instructor will be the “trained” individual and will know that all machines are off or unplugged before turning on the circuit.
The wiring is fine.
You probably don't need to disconnect the Neutral, depending on the earthing system.
In fact, you don't even need a contactor.
We don't know what the instructor is trained in, he may be only good at sticking soles on shoes. :)
They have asked for the stop button that needs key to renegage
The contactor would be a N/O with a N/C stop switch.
You don't need a 4 pole contactor, a double would be fine or as said even a single depending on the earthing system.
So not an emergency stop at all then!
You just need a normal switch operating a contactor
Reply to Contactor wiring, break ring circuit through a stop button in the UK Electrical Forum area at ElectriciansForums.net
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
4K
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Hi Everyone, hoping someone will be able to help me decipher the wiring for this hoist controller. the handset it came with has stopped working...
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...