OK,
You will need four contactors to do what you are trying to do (for the heater part alone).
You will need two self latching contactors (one for each heater), use one of the unused pair of contacts off of each of your start/stop contactors, ie. ones not used in the latch circuit, to feed a switched supply in series with the thermostatic controlled contactor (ie. in series with each thermostat and coil).
This way you can independantly control each heater, and each thermostat can control the second contactor independent from the latch (stop/start) contactor.
It is difficult to put into words, I may see if I can draw it for you.
That would be fantastic.