Had issues with a 240v to 120v control transformer not supplying power to 2 cooling fans. Both fans were connected to transformer via X1 and X2 wiring. X2 wiring was not bonded to ground initially. After bonding X2 to ground, fans would run. Any explanation would be great.
 
Shouldn't X2 be grounded anyway? One theory you have lost the neutral (X2) at the fans and by grounding the transformer it has somehow resolved it.
 
Shouldn't X2 be grounded anyway? One theory you have lost the neutral (X2) at the fans and by grounding the transformer it has somehow resolved it.
Yes I believe that x2 should be grounded but wouldn’t you still have 120 volts between x1 and x2 off the transformer and thus power to run the fans?
 
I don't suppose the fans are grounded to one terminal.
 
Yes I believe that x2 should be grounded but wouldn’t you still have 120 volts between x1 and x2 off the transformer and thus power to run the fans?
It sounds like the transformer is good. You need to check continuity of X2 from the transformer to the fan motors.
 
Alright, definitely something to check. If the continuity were to be good. Should these fans be able to run even if x2 wasn’t grounded then?
Hard to say without being there. Have the fans ever run or is this a new installation.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Taber

Thread Information

Title
Control transformer
Prefix
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
Brett1,
Last reply from
westward10,
Replies
6
Views
1,340

Advert

Back
Top