When i was in college they taught us to use a heat resistant flex for cooker and hob installations and for a hob to use 6mm cable if it will fit but if not 4mm but there was a calculation to work it out exactly although I can't remember it I just asked a friend who's a sparky and he said the 4mm would be fine for the hob and the 2.5mm heat resistant would do for the oven but what the kitchen fitter has used is not heat resistant and as for the testing of the existing work I was taught to atleast use the basic testing procedures: continuity, polarity, continuity of CPC and insulation resistance and as far as fitting a spur goes I'm a plumber I have to fit spurs /QUOTE]
Well I prefer to work to the regulations which permit the use of T&E for the connection of cookers.
That is a ridiculous way to size a cable, using the biggest which fits!
Do you fit ferrules to the ends of the flex? Or do you just put an unprotected fine stranded conductor into screw terminals?
That's a start to testing, but without an earth fault loop impedance test how on earth are you going to know whether there is an earth there at all or if the fuse/mcb will operate? There's no point having a nice continuous CPC if it's not actually connected to earth.
You don't have to fit spurs,