David.

hey chaps,

do you need to put crimped connections covered with new heat shrink into an enclosure?? Connections are above a suspended ceiling and i know i could have got away with choc box etc as its accessible but i didnt :rolleyes:

thanks
 
I would do one or the other - either crimp and heat shrink, or in an enclosure using terminal or wago connectors.
Doing both seems like you're getting the worst of both.
 
crimped and heatshrunk is classed as permanent connection so no, the heatshrink replaces the insulation, nothing wrong either way, as hightower says one way or the other will suffice.
 
Surley all electrical joints & connections need to go in a suitable enclosure.

ian

So should cables. As a general rule if the cables are suitably enclosed the crimps will be as well, often even without heat shrink.
I suppose the exception would be outdoors, in which case I'd use an IP rated enclosure, but probably with wagos or terminal connectors in it.
 
i have never been sure on the crimping situation, because the for example on t+e the grey sheath is your basic protection. if you crimp join does this not show insulation of the cores and therfore have no basic protection? i always crimp joints but have never done so outside of a enclosure etc, just wondered what you guys thought?
 
Surely you mean 'mechanical protection' rather than 'basic protection'?
I reckon heatshrink would replace the mechanical protection of the outer sheath of the t&e.
 
Surely you mean 'mechanical protection' rather than 'basic protection'?
I reckon heatshrink would replace the mechanical protection of the outer sheath of the t&e.

yes i mean mechanical protection, as insulation is basic right? i get muddled with that, yeah i guess the heat shrink would, i never do crimps unless in an enclosure but just wondered. :confused:
 
Basic is protection under normal circumstances when all is well, so both insulation and barriers & enclosures.
Fault protection is protection under fault conditions, eg ADS or double insulation.
 

Reply to Crimp connections in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top