Due to a burnt out 80a rcd on a wylex split board consumer unit, the consumer unit now only has one 80a rcd which all circuits (mcbs) are wired to, so a new 80a rcd has been bought to reinstate the split board. The issue is that the original live and neutral cables that linked the mcbs together have mistakenly been thrown out what is the actually csa if these cables? I don't want to obviously buy an old consumer unit off eBay just for these two short cables but I have found a supplier of various sized awg cables and I'm guessing these should do the job of the original linked cables? Any advice is appreciated
 
Not used Wylex boards are they solid links or flex type cables ?
But as long as the cable can take 80amps ie 16mm and above it wouldn't matter.

Thanks for your reply bryanh, they are the stranded type that run from the neutral block to the fuses etc the strands are normally crimped by the manufacturer into a long metal point for ease of use when terminating into the rcd itself.
 
buy a plastic wylex split load board with 2 RCDs, no MCBs. pinch the tails . cost is peanuts and you'll have 2 RCDs for stock.
 
MK Split Load Kit - Toolstation

You can pick up cable kits for a few quid too. Not sure of the length, but maybe Wylex do a similar kit to match ?

Thanks folks for your advice. I tried to find a cheap wylex split load board but couldn't find one cheap enough to justify the situation so I headed to screwfix and got an MK split load kit which was about 6 quid and includes 2 neutrals and a live, perfect!
 

Reply to csa of wylex rcd live and neutral link cables in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
581
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi Recently my son complained that he was getting shocks from his laptop when plugged into the mains in his room. I checked the socket and the...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock